In any Industry, Which voltage level either 3.3kV or 6.6KV
to be chosen? Then I would like to know ,Is there any cost
consideration or Rating of motor?
Answer Posted / kapil narayanrao bahadure
In any Industry, voltage level either 3.3kV or 6.6KV its
not chose the motor ratings.voltage level in any industry
depend upon total load of industry.firstly total load of
industry consideration & after voltage level consider.
| Is This Answer Correct ? | 3 Yes | 0 No |
Post New Answer View All Answers
The Q-facr o of a coil given as wL/R. what will be shape of Q versus frequency graph.
hi everybody how to design string combiner box (scb) internal parameters like bus bar and spd (surge protection device and fuse which place to set that,and also bus bar one particular cross sectional how much heat generated and how much power loss tell me Clearly and briefly
Which of the following alternatives will be cheaper (1) A 100 h.p AC, 3-phase motor (2) Four motors of 25 h.p each (3) Five motors of 20 h.p each (4) 10 motors of 10 h.p each explain
is that a problem if i connect a single phase load to a secondry delta connected transformer but i get a neutral from other transformer i the system?
What is difference between start imitation and start interlock for 3 phase motor protection ?
Which power will flow first if we switch on a motor Active or Reactive? How?
what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?
what rectifiers is and what are the types of rectifiers?
Refernce currents are to be generated using refernce cueernts how can this be done??
what is the use of vcb & isolator in substation?
which of the following elements is not present in stainless steel
When color of silica gel will gets change from blue to pink from Top to bottom?
How to test IR testing & magnetic balance test
What should be setting for alarm,tripping and cooling fan on for power transformer's oil temp. and winding temp. indicator?
what is the formula for calculating the phase clerance between two phases and phase to earth how to calculate the cable for a motor