Answer / vimal m
Transformer Ratio Test
The performance of a transformer largely depends upon perfection of specific turns or voltage ratio of transformer. So transformer ration test is an essential type test of transformer. The voltage should be applied only in the high voltage winding in order to avoid unsafe voltage.
Procedure of Transformer Ratio Test
First, the tap changer of transformer is kept in the lowest position and LV terminals are kept open.
Then apply 3-phase 415 V supply on HV terminals. Measure the voltages applied on each phase (Phase-phase) on HV and induced voltages at LV terminals simultaneously.
After measuring the voltages at HV and LV terminals, the tap changer of transformer should be raised by one position and repeat test.
Repeat the same for each of the tap position separately.
The above transformer ratio test can also be performed by portable transformer turns ratio (TTR) meter. They have an in built power supply, with the voltages commonly used being very low, such as 8-10 V and 50 Hz. The HV and LV windings of one phase of a transformer are connected to the instrument, and the internal bridge elements are varied to produce a null indication on the detector.
| Is This Answer Correct ? | 0 Yes | 0 No |
this is a special test.refer to manufacturer.
| Is This Answer Correct ? | 2 Yes | 4 No |
how we do Vector group ,magnetic balance and tap changer test in Transformer?
why we use delta connection in transformer
if dc is better then ac...then why we are perfering ac over dc?eg:at home?
wich timer i have prefred for pusher operation fwd & back?
A 3ph load of 10 KW is equal to how many KW of single phase .
for a 400kv t/m line with 10 ampere current will corona occur?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
what is the all safty name of diesel genrator?
xfhnchncv?
how can we calculate fault current of a line in a 6 bus syatem if the faulted line is known?
what is the diffrence between mcb &elcb?
What is the difference between Ceiling Fan armature and Tablefan Armature or winding.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)