Motor also having losses, we call KW rating. In
transformer and generator having losses but we call KVA
Rating why?
Answers were Sorted based on User's Feedback
Answer / ashli
in transformer core loss depends on voltage n cu loss
depends on current and power factor has no influence..
so we express in kva rating
in case of motor rotational loss, loss due to friction
windage loss etc are present. we cant express these losses
in kva
| Is This Answer Correct ? | 33 Yes | 10 No |
Answer / shanmugam
Basically, transformer losses always depending the rated
voltages & rated current. Because the core losses
calculated by open circuit method with full rated voltages
& the copper losses calculating by short circuit method
with full rated current.The losses of transformer is
depending the voltages(V) & current(A).Hence, we saying the
transformer capacity in KVA. The above not in motor
| Is This Answer Correct ? | 22 Yes | 6 No |
Answer / adnan kauchali
Simplest and Guaranteed answer is :
KW and KVA are Active power and apparent power resp.
where Active power(W) needs Power factor known
and apparent power is without power factor.
The Motor's power factor is known so it can be written in
Active Power rating
where in case of generator, there are several connected
loads having different power factor, so we can't calculate
the mean power factor of connected loads hence its rating is
without power factor ; that is VA (volts x amp)
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tameshwar singh
I think that motor is designed for any defined power o/p &
its load Pf is also known for that power thus we can give
its rating in kW. But in case of Xmer & alternator the load
is not fixed & so as the load PF thus its rating is given
in KVA.
| Is This Answer Correct ? | 10 Yes | 10 No |
Answer / raja
the main difference between the kw and kva is the power
factor
kw= v*I*cos@
kva=v*I
| Is This Answer Correct ? | 6 Yes | 9 No |
Answer / dpk_1fj
Motor having a fixed output,we cannot increase,while
transfor depend on what type of load going to be connect on
that,that's why transformer rating alweys in kVA.
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / n.chandra shekar
transformer core lose find by using apply only rated voltage
and copper lossees find out by applying full load current,so
we obtaian exact performance in case motor added a
rotational losees so that it will measuredin kw.tranformer
measured in kva it is fixed .negligible p.f
| Is This Answer Correct ? | 0 Yes | 4 No |
Answer / sumajan
I think In transformer & in generator the PF will be vary
depending up on the load connected with it, in motor it is
a inductive load & we can guess its PF, Usually for
inductive load PF will be 0.8 lagging.
| Is This Answer Correct ? | 0 Yes | 8 No |
Answer / gunasekaran
motor output is mechanical so KW.
transformer is electrical output so KVA.
| Is This Answer Correct ? | 4 Yes | 24 No |
For what purpose an AVR in generator sensing generator output voltage?and how the sensing is done by AVR?
respetsed sir, i have applied for section engg and juniour engg for both chennai and tiruvunabthapur boards for electrical deportments . can u suggest what books i have to follow and and also from which sections they r going ask (i mean weightage and what topics i have to cover) for both se and je for both chennai and tiruvunanthapur boards.......
what is the eight bit unit?
how to find 5 kilo meter long under ground 33 kv cable fault location if IR VALUE shows 0.05 M ohm @5000 volt.and cable fault locator shows some time fault distance 3 kilo meter ,3.7 kilo meter and some time 1 kilo meter? now how to find the fault location that where is leakage.
On PVC conduit the class "A" "B" or "C" is marked what does it shows. Either its thickness or its composition?
What is the difference between earth and neutral
4 Answers ABB, Tamboli Engineers,
How much current will a 5 HP delta connected motor at no load will take?Is tat need a starter
what is pilot wire protection? wer is it using?
how to calculate the change over time for star delta starter for different KW motor?
how can maintaince the acb contactor moveing and fixing kit
Show formula which gives full load current 4.8 amps of a 3 HP motor and 27 amps of a 20 HP motor having 3 phase 460 volts, 0.8 Pf.
what is the difference between relay, contactor
4 Answers BRSS, Vishay Intertechnology,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)