Motor also having losses, we call KW rating. In
transformer and generator having losses but we call KVA
Rating why?
Answers were Sorted based on User's Feedback
Answer / ashli
in transformer core loss depends on voltage n cu loss
depends on current and power factor has no influence..
so we express in kva rating
in case of motor rotational loss, loss due to friction
windage loss etc are present. we cant express these losses
in kva
Is This Answer Correct ? | 33 Yes | 10 No |
Answer / shanmugam
Basically, transformer losses always depending the rated
voltages & rated current. Because the core losses
calculated by open circuit method with full rated voltages
& the copper losses calculating by short circuit method
with full rated current.The losses of transformer is
depending the voltages(V) & current(A).Hence, we saying the
transformer capacity in KVA. The above not in motor
Is This Answer Correct ? | 22 Yes | 6 No |
Answer / adnan kauchali
Simplest and Guaranteed answer is :
KW and KVA are Active power and apparent power resp.
where Active power(W) needs Power factor known
and apparent power is without power factor.
The Motor's power factor is known so it can be written in
Active Power rating
where in case of generator, there are several connected
loads having different power factor, so we can't calculate
the mean power factor of connected loads hence its rating is
without power factor ; that is VA (volts x amp)
Is This Answer Correct ? | 3 Yes | 0 No |
Answer / tameshwar singh
I think that motor is designed for any defined power o/p &
its load Pf is also known for that power thus we can give
its rating in kW. But in case of Xmer & alternator the load
is not fixed & so as the load PF thus its rating is given
in KVA.
Is This Answer Correct ? | 10 Yes | 10 No |
Answer / raja
the main difference between the kw and kva is the power
factor
kw= v*I*cos@
kva=v*I
Is This Answer Correct ? | 6 Yes | 9 No |
Answer / dpk_1fj
Motor having a fixed output,we cannot increase,while
transfor depend on what type of load going to be connect on
that,that's why transformer rating alweys in kVA.
Is This Answer Correct ? | 1 Yes | 5 No |
Answer / n.chandra shekar
transformer core lose find by using apply only rated voltage
and copper lossees find out by applying full load current,so
we obtaian exact performance in case motor added a
rotational losees so that it will measuredin kw.tranformer
measured in kva it is fixed .negligible p.f
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / sumajan
I think In transformer & in generator the PF will be vary
depending up on the load connected with it, in motor it is
a inductive load & we can guess its PF, Usually for
inductive load PF will be 0.8 lagging.
Is This Answer Correct ? | 0 Yes | 8 No |
Answer / gunasekaran
motor output is mechanical so KW.
transformer is electrical output so KVA.
Is This Answer Correct ? | 4 Yes | 24 No |
Auto transformer starter gives the same effect as star/delta strater if its turn ratio = A 0.5 B 0.67 C o.66 D 0.577
How can get elongation of 2 k.G aluminium, if elongated aluminium dia is 2.5 mm?
why the stator is not laminated in DC machines?
What are the possible causes of REF operation on a power transformer
how to choose the cable size for 100A(is there any formula please update)
v=r*i this means when voltage increases current also increases at constant resistance.... p=v*i this means when voltage increases current decreases to maintain the power constant which one is true...
What is a soft start?
How to calculate the copper in HT motors if KW, RPM & Voltage is given
0 Answers Control Dynamics, NTPC,
how we can save the power ? suppose the electricity board gives 11 kw , but the machine require only 8 kw means how we can save the exese energy
60 watt bulb and 1500watt iron which device has more resistance & why
What is Meant by Load factor in Power plant?
why motor range is available 22kv,30kv,37kv,45kv and so on? why motor range is not available 21kv,24,25,26,27kv and so on?