Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


what is pf. how to calculate capacitor bank value to
maintain unity pf.

Answers were Sorted based on User's Feedback



what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / nilesh kumar singh

Power Factor is defined as the ratio of Real power and
Apparent power.

for calculating Capacitor bank value the formula is :

kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}

Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.

Is This Answer Correct ?    101 Yes 8 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / rajendra singh

for calculating Capacitor bank value the formula is :

kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}

Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.

Is This Answer Correct ?    42 Yes 8 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / shivappa

to calculate desired capacitor value, the formula is

KVAR= KW(TAN PHI 1 - TAN PHI 2 )

WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR

Is This Answer Correct ?    23 Yes 14 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / kim leang

KVAR= KW(TAN PHI 1 - TAN PHI 2 )

WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR

Is This Answer Correct ?    14 Yes 9 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / midhun

Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)

Is This Answer Correct ?    6 Yes 1 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / fancy102

hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..

Is This Answer Correct ?    40 Yes 36 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / ezzuddin

The correct answer and below is the proof of the formula:

KVAR= KW X [&#8730;(1–(COS&#1060;)^2)]/COS&#1060;

The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
Tan&#1060;= opposite/adjacent = S/P -----> S=P x(Tan&#1060;)
Pf=COS&#1060;= adjacent/hypotenuse = P/Q ---->Q=P/COS&#1060;
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COS&#1060;)^2= P^2 + (P^2 x (Tan&#1060;)^2)
by divide P^2:
1/(COS&#1060;)^2 = 1 + (Tan&#1060;)^2
by changing the both sides:
(Tan&#1060;)^2 = (1/(COS&#1060;)^2) - 1
(Tan&#1060;)^2 = (1/(COS&#1060;)^2) - ((COS&#1060;)^2/(COS&#1060;)^2)
by Taking the (1/(COS&#1060;)^2) Common factor:
(Tan&#1060;)^2 = {1/(COS&#1060;)^2)} x ( 1 - (COS&#1060;)^2)
by taking the square root:

Tan&#1060; = [&#8730;(1–(COS&#1060;)^2)]/COS&#1060;

so that:
KVAR = KW x [&#8730;(1–(COS&#1060;)^2)]/COS&#1060;

Is This Answer Correct ?    5 Yes 1 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / santosh

react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load

Is This Answer Correct ?    14 Yes 11 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / vekuva

KVAR= KW(TAN PHI 1 - TAN PHI 2 )

WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR

Is This Answer Correct ?    5 Yes 2 No

what is pf. how to calculate capacitor bank value to maintain unity pf...

Answer / ezzuddin

The correct answer and below is the proof of the formula:

KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;

The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:

TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;

so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;

Is This Answer Correct ?    4 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

please send me the previous year's question papers of jindal GET exams

0 Answers   Jindal,


why capacitor burst?

2 Answers  


if acapacitor connected to power supply will it cosume power& will it going to get recorded in energy meter

2 Answers  


What is conventional thermal current (Ith)

0 Answers   Alstom, HPL,


How can I calculate per unit (KWH) fuel (Gas/ Diesel both) consumption 1MW unit?

0 Answers  


Which contains in POLE ASSEMBLY of a 11KV Kirloskar-make SF6 (Model No-FP620A12)? Will u clarify with drawing?

0 Answers   Kirloskar,


Can a generator rated 400 V, 60 Hz be used in a 50 Hz System? Yes or No ? Why ?

1 Answers   VECL,


why we store only dc in batteries ?

1 Answers  


What is a Single Phase and Three phase Power? How it will be converted or transformed into another form?

3 Answers  


At full load wat is the motor p.f And at no load will is the motor p.f?

0 Answers   GEPL,


what is power factor? whether it should be high or low? why?

11 Answers  


without name plate detail of blower how we can find out the HP & Rpm ? the input voltage is 230v single phase

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)