Answer / nilesh kumar singh
Power Factor is defined as the ratio of Real power and
Apparent power.
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 101 Yes | 8 No |
Answer / rajendra singh
for calculating Capacitor bank value the formula is :
kVAr = KW {tan(cos^-1 Phi e) - tan(Cos^-1 Phi d)}
Where - Phi e = existing Power Factor.
Phi d = Desired Power Factor.
| Is This Answer Correct ? | 42 Yes | 8 No |
Answer / shivappa
to calculate desired capacitor value, the formula is
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 23 Yes | 14 No |
Answer / kim leang
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR
PHI 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 14 Yes | 9 No |
Answer / midhun
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / fancy102
hi..i also interested in it..i am carrying out pf
measurement system and i am headache in how to maintain the
unity pf too..
| Is This Answer Correct ? | 40 Yes | 36 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [√(1–(COSФ)^2)]/COSФ
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
Q is the hypotenuse.
S is the opposite.
P is the adjacent.
TanФ= opposite/adjacent = S/P -----> S=P x(TanФ)
Pf=COSФ= adjacent/hypotenuse = P/Q ---->Q=P/COSФ
Pythagoras said that:
Q^2= P^2 + S^2
P^2/(COSФ)^2= P^2 + (P^2 x (TanФ)^2)
by divide P^2:
1/(COSФ)^2 = 1 + (TanФ)^2
by changing the both sides:
(TanФ)^2 = (1/(COSФ)^2) - 1
(TanФ)^2 = (1/(COSФ)^2) - ((COSФ)^2/(COSФ)^2)
by Taking the (1/(COSФ)^2) Common factor:
(TanФ)^2 = {1/(COSФ)^2)} x ( 1 - (COSФ)^2)
by taking the square root:
TanФ = [√(1–(COSФ)^2)]/COSФ
so that:
KVAR = KW x [√(1–(COSФ)^2)]/COSФ
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / santosh
react power kvar=v i sin phi, we know p.f=1,i.e cos phi
calculate sin phi,v i values from total load
| Is This Answer Correct ? | 14 Yes | 11 No |
Answer / vekuva
KVAR= KW(TAN PHI 1 - TAN PHI 2 )
WHERE PHI 1 = EXISTING POWER FACTOR ANGLE i.e., COS^¯1(p.f1)
PHI 2 = REQUIRED POWER FACTOR ANGLE i.e., COS^¯1(p.f2)
p.f 1 = EXISTING POWER FACTOR
p.f 2 = REQUIRED POWER FACTOR
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / ezzuddin
The correct answer and below is the proof of the formula:
KVAR= KW X [Sqrt(1–(CosQ)^2)]/CosQ;
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [Sqrt(1–(CosQ)^2)]/CosQ;
| Is This Answer Correct ? | 4 Yes | 1 No |
What is minimum permicible value of leackage current for LT Panle when applying voltage up to 3 KV for 5 Minuits?
best manufacturer for busbar for outdoor switchyard having double bus bar scheme, can any one share technical specification of busbar. 132kv voltage ?
Define sensitivity?
where the protection CT in neutral of transformer be located, before bifurcation or after bifurcation and why.
what is the role of frequency in electrical system
Why we use the D-curve MCBs in critical power distrubution.
Why are the voltage levels in a powersystem are 11KV,33KV etc., why not 10KV,30KV?
230v 1 phase Phase and Neutral insert in Bulk water what happens.
Why grounding is generally done in supply end?
suppose generator rating is 50 kw,load is 25 kw,hw much d generator ll generate?what about d remainin power?
why we don't discuss power facter in dc?
what is the difference between direct loading and indirect loading?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)