Answer / shashikant
CALCULATIONS AND TABLES
Calculation and selection of required capacitor rating
Qc = P * {tan [acos (pf1)] - tan [ acos (pf2)]}
Qc = required capacitor output (kVAr)
pf1 = actual power factor
pf2 = target power factor
P = real power (kW)
The table below shows the values for typical power factors
in accordance with the above formula
TARGET POWER FACTOR
0.7 0.75 0.8 0.85 0.9 0.92 0.94 0.96 0.98 1
Actual Power Factor
0,40 1.27 1.41 1.54 1.67 1.81 1.87 1.93 2 2.09 2.29
0,45 0.96 1.1 1.23 1.36 1.5 1.56 1.62 1.69 1.78 1.98
0.50 0.71 0.85 0.98 1.11 1.25 1.31 1.37 1.44 1.53 1.73
0,55 0.5 0.64 0.77 0.9 1.03 1.09 1.16 1.23 1.32 1.52
0,60 0.31 0.45 0.58 0.71 0.85 0.91 0.97 1.04 1.13 1.33
0,65 0.15 0.29 0.42 0.55 0.68 0.74 0.81 0.88 0.97 1.17
0,70 0 0.14 0.27 0.4 0.54 0.59 0.66 0.73 0.82 1.02
0.75 0 0.13 0.26 0.4 0.46 0.52 0.59 0.68 0.88
0,80 0 0.13 0.27 0.32 0.39 0.46 0.55 0.75
0.85 0 0.14 0.19 0.26 0.33 0.42 0.62
0,90 0 0.06 0.12 0.19 0.28 0.48
The required capacitor output may be calculated as follows:
select the factor (matching point of actual and target
power factor) k
calculate the required capacitor rating with the formula:
Qc = k * P
Example:
actual power factor = 0.70, target power factor = 0.96,
real power = P = 500kW,
Qc = k * P = 0.73 * 500kW = 365 kVAR
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / cbc
1. PF=Real Power/Apparent Power or PF=KW/KVA
2. a.) (KVAR1)*2 = (KVA1)*2 - (KW1)*2
b.) (KVAR2)*2 = (KVA2)*2 - (KW1)*2
c.) REQ'D KVAR= KVAR1-KVAR2
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / ezzuddin
SORRY FOR THE ABOVE WRONG INFO AND The correct answer AS
STATED below is the proof of the formula:
KVAR= MAX Demand X [TanQ1 - TANQ2];
TanQ1= [Sqrt(1–(CosQ1)^2)]/CosQ1
TanQ2= [Sqrt(1–(CosQ2)^2)]/CosQ2
The proof:
Pythagoras Theorem states that in a right-angled triangle
the square of the hypotenuse is equal to the sum of the
squares of the other two sides.
so that:
C is the hypotenuse.
S is the opposite.
P is the adjacent.
TanQ= opposite/adjacent = S/P -----> S=P x(TanQ;)
Pf=CosQ;= adjacent/hypotenuse = P/C ---->C=P/CosQ;
Pythagoras said that:
C^2= P^2 + S^2
P^2/(CosQ)^2= P^2 + (P^2 x (TanQ)^2)
by divide P^2:
1/(CosQ)^2 = 1 + (TanQ)^2
by changing the both sides:
(TanQ)^2 = (1/(CosQ)^2) - 1
(TanQ)^2 = (1/(CosQ)^2) - ((CosQ)^2/(CosQ)^2)
by Taking the (1/(COSQ)^2) Common factor:
(TanQ)^2 = {1/(CosQ)^2)} x ( 1 - (CosQ)^2)
by taking the square root:
TanQ; = [Sqrt(1–(CosQ)^2)]/CosQ;
so that:
KVAR = KW x [TanQ1 - TANQ2]
example:
PF1 = CosQ1 = 0.8
PF2 = CosQ2 = 0.92
TanQ1 = 0.75
TanQ2 = 0.426
P=1000 KW
Max Demand = 1000x0.8= 800 kW
Capacity of the required Capacitor= 800 x(0.75 - 0.426)=
264 KVAR
We proposed automatic capacitor= 300 KVAR
Is This Answer Correct ? | 4 Yes | 4 No |
Answer / sm
pf is the cosine of the angle b/w voltage phasor and current phasor. To maintain unity feedback the capacitor bank value should be such that it compensates the inductive reactance value in circuit i.e., X becomes zero. Thus, the circuit becomes purely resistive and pf is unity.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rukmagoud
Required Capacitor bank and required KVAR of the bank to be
installed to improve power factor from say x to y is
KVAR=KW(TANx-tany).This can be better understood from power
triangle.
RUKMAGOUD
APGENCO
HYD
Is This Answer Correct ? | 3 Yes | 4 No |
Answer / udayak25
in short I tell u -
kVA
kVAR = -----
0.432
it gives u a correct value of capacitor bank.
-Uday
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / j. nagarajan
The power factor is the ratio of voltage to current at
120Deg Phase shift.
Cos phi = KVA/KW
The active power factor in our country will be 0.8 only, ie
only 80% of power consumed and balance is lost due to
various lossed in the distribution system.
To calculate Cap. bank the formula is
KVAR = Power tan (cos phi(ext)-tan cos phi (exp)
where cos phi(ext) - existing power factor & exp is
expecting power factor.
It is not possible to brought to unity powerfactor is
utilising 100% of power to the application. Max. of 95% can
be possible for which the power factor value will be 0.95
After calculating cap. banks, say 100kvar, it can be
seperated like below:
1:1:1:1 (where 1=25kvar)
1:2:1(where 2=50kvar)... and so on.
- J. Nagarajan
Is This Answer Correct ? | 0 Yes | 4 No |
Answer / hassan azzam
dear all your formula is correct but this for existing
system , wher if you dont have mesured value how to estimat
there use my estimation
Qc (Kvar) = connected load( kw)* 0.8 * 0.75 * 0.421
Qc (Kvar) = connected load (kw) * 0.2526
this is for future load or testing and commissioning perid
Is This Answer Correct ? | 5 Yes | 10 No |
define electrical field?
how to decide the panel size like MDB ,SMDB PANEL SIZES
A well system is when , no. of bus bar is less or more. Tell me the concept of it.
Why not using Air circuit breaker at High tension side?
What are motor generator sets and explain the different ways the motor generator set can be used ?
how we calculate capacitor bank mvar for 11 kv distribution networ , and i need releation between capacitor bank with voltage, frequency, current, pf
What is excitation?
why we use circuit breakers for switching instead of normal switching device?
What is the need of motor starter?
What is vector group? What is meant by DYN11?Why is it needed?
13 Answers Areva, Bhel, BRG, Escorts, Fortis,
What is various types of electrical formula?
What is use of 3phase instead of single phase?
12 Answers DCM, L&T,