why ct is testing using dc.. y cant we use AC insted of dc
on POLARITY TEST.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
Dc is not applied continuously. It is just touch and go, to
create momentary flux.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / raj
then how we are using dc on test ..dc wont step up or step
down.., hw dc is craeting current that was shown in galvano
meter . please explain briefly..?
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / er dhananjay kumar
Actually in dc genertae constant flux. When we puch on buttons the contant have to travel from one side of ct (p1) to another side of ct (p2) and in this traveling. The flux is cut by ct winding all this event exist for micro second and this will induce a little potential across secondary side and in unidirectional that's why meter sow a little deflection
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / raghavendran.r
I think for Polarity testing AC is being used in power transformers.Let me explain the circuit for the same .Keep the secondary side open.But short one of the terminals of the secondary side with the primary side, so that the primary current flows through the secondary.Now adjust the primary voltage using variac and note down the secondary voltage.If primary voltage is greater than secondary then the polarities are different.
If secondary voltage is more than primary then the polarities are same.
This is how polarity is tested in power transformers and Motors.
The same may apply to CT also.
Is This Answer Correct ? | 0 Yes | 1 No |
how could we findout the lightning arrester failed or not in live circuit? Is there any instrument to measure the high voltage at the time of sky lighting?
what is bausbar?
Is there any calculation to find unknwon(unferroled) phases R Y B in alternator,3 phase motor anybody shoot my problem. how can we notice this is the respective phase?
SUTIABLE FOR ohm's law super conductor
define B types and C types in MCB ?
What is meant by Active and reactive power?
23 Answers College School Exams Tests, Schneider, Torrent Power,
why in US MAINTAIN 60hz,110volts when compared with 50hz,220v in india
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
what clearance required for 4.5 mva dry type transformer?
Did RMU have ct and pt ?
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
What is the reason for low voltage in houses?