Procedure for conduting vector group test on power
transformers.why it is conducted?
Answers were Sorted based on User's Feedback
Purpose: The Polarity and Phase relation tests are
importent when two or more transformer are to be
paralleled.Parelleled transformer must have the same
polarity and phase relation to avoid parial or complete
short circuits.
Test Procedure:(Yyn11)
The L.V. vector will be superimposed on H.V. by connecting
1U & 2U Terminals. The three-phase voltage will be applied
to the line terminals of H.V. winding. Voltage measurement
will be done across:
1U-1V:
1V-1W:
1W-1U:
1V-2V: 1V-2W:
1W-2V: 1W-2W:
1U-2N: 1V-2N:
Checks: - 1V-2V = 1V-2W
1W-2V > 1W-2W
1U-2N + 1V-2N = 1U-1V
| Is This Answer Correct ? | 41 Yes | 14 No |
Answer / pavan
Vector group analysis is done to know the phase displacement.
| Is This Answer Correct ? | 17 Yes | 5 No |
I also wanted to know this. But as per my knowledge, Same
phase of both primary and secondary are to be shorted
before applying voltage in the answer given by Mr.
Maheshreddy.
Please let me know am I correct?
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / gunasekaran
this is important for parallel operation vector group should
be same another one is vector group is changed polarity of
the transformer also change it YNyn0 become YNyn6 if it is
changed
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / r. n. aggarwal
It is conducted to ascertain the polarity and phase
displacement.
The polarity of two transformer having the same vector
group must be same.
A further check to confirm that the polarity or phase
displacement ( vector group ) of two transformer is the
same.A single three phase LT supply is fed to the HT side
of Transformers and the same phase of the LT suppy must be
connected to the corresponding HT terminals of
Transformers .Then the voltage is checked on LT terminals
of transformers with multimeter between the same phases and
it should read almost zero.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anil k panjani
I would like to know the test procedure for Dyn11 vector
group and the conditions to be met for the same
| Is This Answer Correct ? | 2 Yes | 0 No |
In three pin socket normally three pin in between three pins earthing point is more thickness why?
when a machine act as genartor and as motor?
what is the current carrying capacity of 725 va generator
what is differnt between metering CTs an protection CTs
What is the different between feeder & bus?
what are the preventive maintanance actions taken for air circuit breaker? please answer me
what is the range of thermal overload and over current. Answer should be in percentage of current.
What is the difference between vector surge relay (78) and Pole slip relay (98G)
Is itnecessary to use capacitor in an Fluorescent Tube Light Fixtures? Why? What if not capacitors are not included?
what is amf panel & how it is working
what is different the DOL Starter and Star Delta STARTER
What is stray looses?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)