Procedure for conduting vector group test on power
transformers.why it is conducted?
Answers were Sorted based on User's Feedback
Purpose: The Polarity and Phase relation tests are
importent when two or more transformer are to be
paralleled.Parelleled transformer must have the same
polarity and phase relation to avoid parial or complete
short circuits.
Test Procedure:(Yyn11)
The L.V. vector will be superimposed on H.V. by connecting
1U & 2U Terminals. The three-phase voltage will be applied
to the line terminals of H.V. winding. Voltage measurement
will be done across:
1U-1V:
1V-1W:
1W-1U:
1V-2V: 1V-2W:
1W-2V: 1W-2W:
1U-2N: 1V-2N:
Checks: - 1V-2V = 1V-2W
1W-2V > 1W-2W
1U-2N + 1V-2N = 1U-1V
| Is This Answer Correct ? | 41 Yes | 14 No |
Answer / pavan
Vector group analysis is done to know the phase displacement.
| Is This Answer Correct ? | 17 Yes | 5 No |
I also wanted to know this. But as per my knowledge, Same
phase of both primary and secondary are to be shorted
before applying voltage in the answer given by Mr.
Maheshreddy.
Please let me know am I correct?
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / gunasekaran
this is important for parallel operation vector group should
be same another one is vector group is changed polarity of
the transformer also change it YNyn0 become YNyn6 if it is
changed
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / r. n. aggarwal
It is conducted to ascertain the polarity and phase
displacement.
The polarity of two transformer having the same vector
group must be same.
A further check to confirm that the polarity or phase
displacement ( vector group ) of two transformer is the
same.A single three phase LT supply is fed to the HT side
of Transformers and the same phase of the LT suppy must be
connected to the corresponding HT terminals of
Transformers .Then the voltage is checked on LT terminals
of transformers with multimeter between the same phases and
it should read almost zero.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anil k panjani
I would like to know the test procedure for Dyn11 vector
group and the conditions to be met for the same
| Is This Answer Correct ? | 2 Yes | 0 No |
We have Diesel generator of 200KW but load connected to it only 100KW. Pl. brief me about fuel consumption.
Brief use of isolation transformer & how it works.
why zero sequence impedance measurement is not applicable for single phase GT
what is the diff. between AVR & H.T.Stabilizer
is tree is a good conductor and it may be used for conductor?
how to do the ductor test?
What should be the DC voltage for Hi-pot test on 11kv switchgear
List advantges of active filter over passive filter?
how to select the isolation tranformer for siemens 802dsl cnotroller
an off load but energized 11/0.4 KV, 1250 KVA T/F has a power factor of 0.65(capacitive)..!! why is it so, though T/F being an inductive device ??
draw vector diagram and +ve,zero sequence diagram of symmetrical three phase fault.
what is power factor in ac ckt ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)