Procedure for conduting vector group test on power
transformers.why it is conducted?
Answers were Sorted based on User's Feedback
Purpose: The Polarity and Phase relation tests are
importent when two or more transformer are to be
paralleled.Parelleled transformer must have the same
polarity and phase relation to avoid parial or complete
short circuits.
Test Procedure:(Yyn11)
The L.V. vector will be superimposed on H.V. by connecting
1U & 2U Terminals. The three-phase voltage will be applied
to the line terminals of H.V. winding. Voltage measurement
will be done across:
1U-1V:
1V-1W:
1W-1U:
1V-2V: 1V-2W:
1W-2V: 1W-2W:
1U-2N: 1V-2N:
Checks: - 1V-2V = 1V-2W
1W-2V > 1W-2W
1U-2N + 1V-2N = 1U-1V
| Is This Answer Correct ? | 41 Yes | 14 No |
Answer / pavan
Vector group analysis is done to know the phase displacement.
| Is This Answer Correct ? | 17 Yes | 5 No |
I also wanted to know this. But as per my knowledge, Same
phase of both primary and secondary are to be shorted
before applying voltage in the answer given by Mr.
Maheshreddy.
Please let me know am I correct?
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / gunasekaran
this is important for parallel operation vector group should
be same another one is vector group is changed polarity of
the transformer also change it YNyn0 become YNyn6 if it is
changed
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / r. n. aggarwal
It is conducted to ascertain the polarity and phase
displacement.
The polarity of two transformer having the same vector
group must be same.
A further check to confirm that the polarity or phase
displacement ( vector group ) of two transformer is the
same.A single three phase LT supply is fed to the HT side
of Transformers and the same phase of the LT suppy must be
connected to the corresponding HT terminals of
Transformers .Then the voltage is checked on LT terminals
of transformers with multimeter between the same phases and
it should read almost zero.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / anil k panjani
I would like to know the test procedure for Dyn11 vector
group and the conditions to be met for the same
| Is This Answer Correct ? | 2 Yes | 0 No |
how to calculate the cable size in sqmm if load (kw) is given?
When we giving the 3 phase supply to ups system how to coming netural?
0 Answers Juniper Networks, Tata Motors,
cable selection formulas for electrical load.
I have raw material for making Compact-Choke for flourscent lamp of 40 Watts. We are suppose to get 0.4 amps output at end. but we are getting 0.42 or 0.44 amps and above. We have done many testings in different but nothing worked out. Please suggest me how to get the correct output. We are using 1. core winding of 700 windings of aluminium 2. E-shape iron fillings and I-shape iron fillings to surround the winding.
basic differance between electrical and electronic.
what are the method of testing of transformer??
what is saturation in transformer
my diploma certificate in my higher education college
which plant has high load factor
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,
how can we find of cable capicity in amper?how much ampere withstand by 300sqmm cable?
what are the needs of electrical earthing.... other than protection?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)