Procedure for conduting vector group test on power
transformers.why it is conducted?

Answers were Sorted based on User's Feedback



Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / maheshreddy

Purpose: The Polarity and Phase relation tests are
importent when two or more transformer are to be
paralleled.Parelleled transformer must have the same
polarity and phase relation to avoid parial or complete
short circuits.

Test Procedure:(Yyn11)
The L.V. vector will be superimposed on H.V. by connecting
1U & 2U Terminals. The three-phase voltage will be applied
to the line terminals of H.V. winding. Voltage measurement
will be done across:
1U-1V:
1V-1W:
1W-1U:

1V-2V: 1V-2W:
1W-2V: 1W-2W:
1U-2N: 1V-2N:



Checks: - 1V-2V = 1V-2W
1W-2V > 1W-2W
1U-2N + 1V-2N = 1U-1V

Is This Answer Correct ?    41 Yes 14 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / pavan

Vector group analysis is done to know the phase displacement.

Is This Answer Correct ?    17 Yes 5 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / suresh kumar

I also wanted to know this. But as per my knowledge, Same
phase of both primary and secondary are to be shorted
before applying voltage in the answer given by Mr.
Maheshreddy.
Please let me know am I correct?

Is This Answer Correct ?    14 Yes 5 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / gunasekaran

this is important for parallel operation vector group should
be same another one is vector group is changed polarity of
the transformer also change it YNyn0 become YNyn6 if it is
changed

Is This Answer Correct ?    6 Yes 1 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / r. n. aggarwal

It is conducted to ascertain the polarity and phase
displacement.

The polarity of two transformer having the same vector
group must be same.

A further check to confirm that the polarity or phase
displacement ( vector group ) of two transformer is the
same.A single three phase LT supply is fed to the HT side
of Transformers and the same phase of the LT suppy must be
connected to the corresponding HT terminals of
Transformers .Then the voltage is checked on LT terminals
of transformers with multimeter between the same phases and
it should read almost zero.

Is This Answer Correct ?    3 Yes 0 No

Procedure for conduting vector group test on power transformers.why it is conducted?..

Answer / anil k panjani

I would like to know the test procedure for Dyn11 vector
group and the conditions to be met for the same

Is This Answer Correct ?    2 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

.if the vector group of two transformers is not same n tey r connected in parallel operation then what will happen?

2 Answers   ABB,


why two fuses are used in battery charging room?one in positive line and the other in negative line?do any DC system require two fuses?

1 Answers   HPCL,


How the power factor is more in high speed machines

1 Answers  


Can anybody tell me what the breakdown voltage is for air and what it is for transformer oil please?

4 Answers   Pooja Cables,


Define the term factor of inertia.

0 Answers  






WHY CAPACITOR IS NOT USED FOR THREE PHASE MOTORS DURING STARTING

1 Answers   Quest,


Why short ckt does not happen when solenoid coil connected to supply. as its a wire only.

1 Answers   Siemens,


Can we use shunt trip coil instead of trip coil with protection relay for protection?

0 Answers  


why in dc generator field rheostate kept in maximum position?

1 Answers  


What are the details of ratings of different types of ACSR conductors?

2 Answers  


Why 11KV/440V distribution supply use for Domestic use?

3 Answers   Essar, Getco, Nissan,


What is Lockout Relay and what is use of it in electrical installation

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)