At first calculate the current of the load, after that
derate the current considering derating factor(depending
on site condition and laying of cable) after choose the
cable size from cable catalog considering derating current.
After that measure the length of cable required from supply
point of load to load poin. Calculate the voltage drop
which will max 3% (resistance and reactance of cable found
from cable catalog of selecting cable) if voltage drop>3%
then choose next higher size of cable.

Is This Answer Correct ?    5 Yes 0 No

How do you select a cable size(Cu & Al) for a particular load?..

Answer / santhosh k.m

actualy we take cables in current rating

1 Sq.mm = 0.8 or 0.9 A for power cables.

Is This Answer Correct ?    2 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

What is the difference between MCB and Earth MCB? What is the working principal of MCB?

2 Answers  


What is d main advantage of using double circuit 3 phase transmission ?

0 Answers   UHG,


What is the use of bundle conductors?

0 Answers  


what will happen if we use earthing inplace of neutral for domestic energy meter

5 Answers   Polyplex Corporation Limited,


What is the acessaries distribution transformer ?

11 Answers   Bhel,






A synchronous motor is operating at a leading power factor .if the applied voltage is decreases ,(the excitation remains constant ) ,the motor current a)increases b) decreases c)remains same d) none of these

2 Answers  


WHAT IS NORMAL VECTOR GROUP USED FOR DESIGNING OF TRANSFORMERS??

11 Answers  


why stator winding of synchronous machine are connected in star connection ?

1 Answers  


Explain Clearly Pahase and Neutral?

7 Answers  


what is the IEC standard for Power Cable installation in onshore (like in direct buried ground or above groung)

0 Answers   L&T,


What the capacitor Current formula?, For 1 KVAr how amps its required? for using the KVAr for boosting the PF Design Calculation.( Eg: for 30 KVAr required how many KW?)

17 Answers   Alstom, Call Centre, EDC, HCL, Procon Engineers,


Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)