How do you select a cable size(Cu & Al) for a particular
load?
Answers were Sorted based on User's Feedback
Answer / mrinal
At first calculate the current of the load, after that
derate the current considering derating factor(depending
on site condition and laying of cable) after choose the
cable size from cable catalog considering derating current.
After that measure the length of cable required from supply
point of load to load poin. Calculate the voltage drop
which will max 3% (resistance and reactance of cable found
from cable catalog of selecting cable) if voltage drop>3%
then choose next higher size of cable.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / santhosh k.m
actualy we take cables in current rating
1 Sq.mm = 0.8 or 0.9 A for power cables.
| Is This Answer Correct ? | 2 Yes | 3 No |
What is earth system using on the floater TN-S or TT. Iam not sure and what ICCP
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
why the altrnator(AVR) not showing the any voltage after making the new winding and insulation?
What is the harm if we install primary side 11 KV VCB at a distance of one Km from the 11/3.3KV 12.5 MVA transformer through 11 KV cable.
Is it true online ups having bypass mode if it is true then why we called ups because it is interrupting power when goes in bypass mode
what will happen to give a dc supply in ac motor?
Explain why inductance of the iron cored coil changes with current?
what is meant by bus bar and outgoing/incoming breaker in an electrical/electronic circuit
what is the basic paramter to set a electric drive
1.what is surge 2.what is lightning 3.what is switching 4.difference between surge,lightning,switching used in power system 4.definition of surgearrestor,lightningarrestor 5.adv and disadv of surgearrestor,lightningarrestor 6.uses and purpose of surgearrestorand lightning arrestor 7.block dia of surge arrestor 8.blockdiagram of lightning arrestor 9.operation and working of surge arrestor and lightning arrestor 10.basic formula of surgearrestor and lightning arrestor 11.basic diagram of surge arrestor and lightning arrestor
1 Answers Crompton Greaves, Framo, L&T,
what is difference between power transformer and distribution transformers
why transformer rating is in KVA?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)