what is diffential relay? testing proceure?and
transformer reach Over load thet time differencilal relay
operate or not ?
Answers were Sorted based on User's Feedback
Dear friends
1.Diff relay compares two currents entering and leaving the
protected equipment or zone in respect of current
maagnitude and phase angle, and if there is any unbalance
or spill current found, that current will flow through the
operating coil of the relay and give trip pulse to the
Circuit breaker to isolate the supply to the transformer.
2.Please note that,Diff relay will operate only for
internal fault of the protected equipment(for
example,winding fault in transformer) and it should not
trip for over load of transformer and any external fault.
please feel free to ask further doubts in this topic.
regards
gova
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / m raviteja
differential relay is the difference of current from
primary and secondary of the transformer.Normally setting
is at 0.6% if more than that the transformer will tripped
on that relay fault.
the primary current and secondary currents are connected to
individual ct's and that terminals are connected to relay.
differential relay is of two types voltage based and
current based.Normally current based is used in industries.
testing procedure:both primary and secondary currents are
induced to relay and make the required setting if current
difference is more than that the relay acts.
differential relay will not operate when overload the
transformer unless the difference in primary and secondary
currents
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sathish
which operates on the basis diffence in currents in
windings.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / engr rb
differential rely operatets on differencs in either voltage
or current, these are two diff relays,. definately if the
transf over loaded then voltage will drop and current will
increase so it will cause imbalace in the current and
voltage cosequently rely will be operated.
| Is This Answer Correct ? | 1 Yes | 3 No |
A three phase load, around 4 km away from the 11/0.433KV distribution transformer (Neutral of Transformer is solidily earthed) and consisting of mainly very costly and sensitive electronic equipments is giving trouble due to high voltage difference between neutral and body earth. Whether this problem can addressed by connecting neutral at the load point solidly to earth?
Define average demand?
Explain cos(theta) and Sin(theta)
Briefly describe means used by electricity suppliers to influence the flow of active and reactive power in power networks (one for each type)?
difference b/w timer and counter
single phase can run in PVC conduit. Three phase can also run in one PVC conduit. But two phase cannot run in one PVC conduit. WHY? reply plz....awaiting your answer.
Can any horizontally mounted motor be used as vertical?
Explain how you can give the overload setting to any Motor Protection Relay for a HT motors with formula and example?
why the India electrical supply transmission loss is high when compare to us
Do you know how to joint the H.T and L.T Cables?
23 Answers KESC, MGVCL, Nokia, Oil Country Tubular, Power Control, SAGT, Siemens, Simco, Vivek Engineers,
How to convert resistance value at 20 degree to 90 degree?
the resistance of wire having length X M is R OHEM if i streched the wire to dubble length what will be the resitance
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)