how to calculate knee point voltage of current transformer?
Answers were Sorted based on User's Feedback
Answer / srinivasan venkatesh.
to calculate the CT Vk .
eg
CT Acc. class - 5p20
sec. ct - rated = 1 A
Rct - 3 Ohms
Burden 15VA
Vk = 20((Rct+Burden))
= 20((3+15 )
= 360V
in the above VK ,Imag critieria is less than 5% of the CT
secondary current. ie - 500mA ( equal to or less than) .
Is This Answer Correct ? | 14 Yes | 12 No |
Answer / arvind negi
Calculation:
1) Fault Current at Primary Side of CT (kA) = MVA/*100(%
Z*1.732*KLV) 7.55
2) Fault Current at Secondary Side of CT, If (A)=
6.29
3) Cable Lead Resistance, RL (Ohm)= 1.02
4) Knee Point Voltage Vk (Volt) = 2If(RCT+2RL)
101.2
REMARKS : -
Knee Point Voltage of CT provided by CGL for REF CT = 115V
and for Differental CT = 200V are in order.
Is This Answer Correct ? | 6 Yes | 6 No |
Answer / muhammad ehsan
I am not familiar with the term saturation test but it seems
from the above posts like an exciting current test to
obtain the knee-point of the CT. With this test you can also
obtain the exciting curve (mag-curve) of the CT.
You'll need a variable voltage, (easiest obtain from a
variac - must be able to obtain the suitable voltage) a
voltmeter, an ammeter, a pencil and paper.You'll have to
measure the voltage and the current while you do the test.
Apply the voltage to the secondary winding with the primary
and other windings being open-circuited. Increase the
voltage until you reach a point where a small increase in
voltage results in a big increase in current.
Now slowly decrease the voltage to a few measuring points,
while you measure the current. (write it down) Something like:
205V - 1.1A
200V - 0.6A
190V - 0.238A
180V - 0.149A
170V - 0.114A
150V - 0.08A
125V - 0.061A
100V - 0.049A
50V - 0.028V
25V - 0.017A
0V - 0A
You have to decrease your voltage slowly to zero volt to
demagnetize the CT-core.
BEWARE The knee-point voltage will depend on the size and
class of the CT, and it can be very high on some CTs
(several hundreds of volts) Be very cautious, you will be
working on live equipment during the test.
Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / ramesh
to calculate knee point voltage of current transformer by
formal
Vknee point = Isecandary(Rct+ Rcable+ Rburden)
where
Rct= resistenc of current transformer
Rcable =resistenc of cable =2Rcable
Rburden =burden of relay
IF Vknee point< manufacture voltage of current transformer
current transformer is good
IF Vknee point> manufacture voltage of current transformer
current transformer must be change
Is This Answer Correct ? | 3 Yes | 3 No |
Answer / mayank trivedi
PRIMARY WDG IS KEPT OPEN. AND VOLTAGE IS APPLIED AFTER
CALCULATING THE KNEE POINT VOLTAGE. I.E BY THE GIVEN FORMULA.
Vk= If(Rct + 2Rl)
SUPPOSE THE KNEE POINT VOLTAGE IS 300 AND SPECIFIED
MAGNETISING CURRENT IS ABOUT 0.65 AS GIVEN ON NAME PLATE.
THAN 10 % VOLTAGE IS APPLIED ON SECONDARY WINDING OF 300V
I.E 30 VOLTS AND THAN INCREASED IN 10 NUMBER OF STEP.
AT FULL KNEE POINT VOLT THE MAG CURRENT SHOULD BE WITHIN
RANGE. THAN ST IS SAID TO PASS THE THE.
THE MAG CURRENT IS MEASURED BY CONNECTING A AMMETER IN SERIES.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / rajkumar
Knee Point Voltage Vk = IFsc * K * (Rct+(2*RL)+Rr)
Where,
IFsc - Fault current at the secondary of CT
IFsc->IFprimary/CT Ratio
IFprimary -> Fault MVA at primary/(1.732*Primary Voltage)
K - Dimensioning Factor
Rct - CT Resistance
RL - Lead Resistance
Rr - Resistance of relay to which CT is connected
Knee point voltage is the voltage at which 10% raise in secondary voltage will result in 50% raise in current..
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / narendra solanki
The knee-point voltage will depend on the size and class of
the CT, and it can be very high on some CTs Be very
cautious, you will be working on
live equipment during the test.
Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.
Is This Answer Correct ? | 5 Yes | 6 No |
Answer / jayachandran
Vk=A*N*0.021*1.6
A= cross sectional Area,
N= No. of Secondary Turns
This is only if you know the cross sectional area and number of secondary turns.
Is This Answer Correct ? | 1 Yes | 2 No |
For calculating knee point voltage there are two methods,
they are
1.Low method
2.High method
1.low impedance method
Vk=24In(Rct+2Rl)
2.High impedance method
Vk=4IsRs
Then, Rs=If/Is(Rct+Rl)
where
Is,In-Rated Sec. Current of CT
Rct-CT resistance
Rl-Max. one way lead reistance from CT to Relay
Is This Answer Correct ? | 9 Yes | 21 No |
Answer / gusu
knee point Voltage = Burden x aLf
-------------
Class
E.g:10VA 5P20 CT.
To Get the Knee Point Voltage
=> 10VA x 20
--------- = 10 x 20
5P ------- = 40V
5
Is This Answer Correct ? | 22 Yes | 49 No |
starting torque is increased and current is decreased by using external resistance in a slip ring induction motor. How??
A system absorbs 100 k J of heat and the increase in its internal energy is 100 kJ; the work done is
why alternator is used instead of dc generator and induction generator
Why does the power consumed is always constant even if a fan speed is altered?
what is the difference between KW and KWh?
Plugging is a phenomenon to= A braking the motor B to accelerate the motor C to run IM as generator D to start the motor
Current Transformer's star point must face the protected object for the relay operation?
I WANT TO INSTALL LIGHTING ARRESTOR ABOVE 20 FEET HEIGHT INDUSTRIAL BUILDING. NOW IT WAS 15 FEET HEIGHT HOW MUCH DISTANCE IT WILL COVER & HOW TO CALCULAT THE DISTANCE COVER BY THE ARRESTOR
What is on line ups and off line ups?
What is the effect of leading power factor for power transformer & D.G?
why dc current is supplied in america rather than ac
What is the suitable rating of MCB used for 1.5 Ton A.C & why?