What is Hi-Pot Test for Grid Station HV Equipments?
Answers were Sorted based on User's Feedback
Answer / naresh chandra jha
Hi-pot test is used to check the leakage current of HT
breaker , Ht bus bar,HT cable .In this test (3v+1)80%
voltage is applied in one phase and leakage current is
measure in other two phase(which is shorted )with the help
of multimeter ,which is connected in hipot kit .In hipot
test ,voltage is step up with the help of auto
transformer(variac) and hipot kit. this hi voltage(AC
voltage for breaker ,bus bar and DC voltage for cable )is
applied in phase. DC voltage is created with the help of
diode which is connected in series with AC voltage(hipot kit) .
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / shao
Thank you so much Naresh!
But i think we only measure the respective leakage current at that phase on which we have applied voltage.?
e-g; Applied 40KV at Red phase for 60sec, & measured leakage current was 0.6micro Amperes.
Actually im seeing this testing at a 132KV Grid Station.
Is This Answer Correct ? | 4 Yes | 0 No |
would you please give me any idea about the BARC interview question on electrical? i have an interview on 1st july.....plz hlp me.......its urgent......
Differentiate between ideal and non ideal current sources?
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
Why hydropower is called renewable source of energy?
if we have 320KVA Genset kindly advice how much load we can put it.
150 hp moter how many kwh in 1 hour and what forfula 3 phase kwh.
5 Answers College School Exams Tests, CPCL, Syncom, Thermax,
can we use metering current transformer as protection current transformer if not why? & if yes why?
sir , what happen if we decrease ( approx 3 inch ) the lenth of shaft in 110KW Induction , three phase motor. actually a 110KW motor is couppled with star couplling to 120TR compressor. When we doing maintenance in compressor it is required to skid the motor backword and resulting dis- alightnment . so we want to change the tyre coupling in place of existing coupling. so it is required to cut off the rotor aprox 3 inch form driving side.
How many no. of earthing pits required for commisioning a new 320KVC DG Set????How????
what is the maximum load on for 10 kva & 25 kva transformer
what maximum range of star & delta in hp or kw ?
0 Answers Makkah Hilton Towers,
Why Generator KVA not in KW ?
3 Answers Bygging India, HHH, Tata Motors, TVS,