Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

how to calculate knee point voltage of current transformer?

Answer Posted / muhammad ehsan

I am not familiar with the term saturation test but it seems
from the above posts like an exciting current test to
obtain the knee-point of the CT. With this test you can also
obtain the exciting curve (mag-curve) of the CT.

You'll need a variable voltage, (easiest obtain from a
variac - must be able to obtain the suitable voltage) a
voltmeter, an ammeter, a pencil and paper.You'll have to
measure the voltage and the current while you do the test.
Apply the voltage to the secondary winding with the primary
and other windings being open-circuited. Increase the
voltage until you reach a point where a small increase in
voltage results in a big increase in current.
Now slowly decrease the voltage to a few measuring points,
while you measure the current. (write it down) Something like:

205V - 1.1A
200V - 0.6A
190V - 0.238A
180V - 0.149A
170V - 0.114A
150V - 0.08A
125V - 0.061A
100V - 0.049A
50V - 0.028V
25V - 0.017A
0V - 0A

You have to decrease your voltage slowly to zero volt to
demagnetize the CT-core.

BEWARE The knee-point voltage will depend on the size and
class of the CT, and it can be very high on some CTs
(several hundreds of volts) Be very cautious, you will be
working on live equipment during the test.

Now you can just plot the current and voltage values on a
graph. This is the mag-curve of the CT. IEC classify the
knee point voltage as the point where a 10% increase in
voltage results in a 50% increase in current.

Is This Answer Correct ?    2 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

Dear All, I am new in construction company , my boss ask a question at time of interview , If we have 60MW generation and Single Power Transformer step-up we have. if CMR 50/60MVA , ONAN, ONAF respectively , is it sufficient or not ? for that much power to transfer,

1610


How to calculate the sag on transmission Lines.

2954


what is a vector protection in transformer

1983


Define availability (operational)?

1114


why are the maintaine power factor and how can this control and this is how work.

1938


What are the types of transformers according to the arrangement of iron cores?

1092


WHAT IS THE FUNCTION OF SHORT CIRCUIT MAINTENANCE CT

2415


Name one of major transformer company in KSA ?

1155


Is there any specialised book to refer about fault level calculation both in MV and LV side??

2041


What is the equivalent circuit of a transformer and its vector diagram?

2657


How to decide whether A / B / C / D curve type MCB should be used?

2256


What is main cause of cable's terminal point burned in Lug on high temperature although lug and cable selection is ok as per stantard and also tightness is ok as per situation. so please take in deep and tell correct answer thanku.

8206


what would happen if reactive power (kvar)is increased (more)or decreased (less)? how much exact reactive power should be maintained? and what should be done for that

2242


Why do we require transformer with less specific weight if supply frequency is increased?

1542


what is working process of star delta controlling circuit ?

1842