how to calculate knee point voltage of current transformer?
Answer Posted / arvind negi
Calculation:
1) Fault Current at Primary Side of CT (kA) = MVA/*100(%
Z*1.732*KLV) 7.55
2) Fault Current at Secondary Side of CT, If (A)=
6.29
3) Cable Lead Resistance, RL (Ohm)= 1.02
4) Knee Point Voltage Vk (Volt) = 2If(RCT+2RL)
101.2
REMARKS : -
Knee Point Voltage of CT provided by CGL for REF CT = 115V
and for Differental CT = 200V are in order.
| Is This Answer Correct ? | 6 Yes | 6 No |
Post New Answer View All Answers
what could be the RMS value and average value of a 4 phase sine wave?
how can i apilly for electrical c licencese.sir,i completed B.Tech in electrical & electronics engineering in 201onot working any company
what is a speed of rotor when we give supply to stator of 50hz and as well as rotor of 60hz of an induction motor?????
What is difference between SMC supportg and Glass Fibre Reinforced Plastic Support.
what is the max. acceptable leakage current in 33kv bus bar
how can i determine the gear ratio for a rack and pinion system if an electronic gate operated by an electric motor is to travel a distance of 5meters in 15 seconds.
What is pd controller?
HOW TO CALCULATE EARTHING SIZING?
Is the installation of the filter cloths necessary before spreading the gravels at the transformer yards?
How to test lightning Arrester?
what is the saturation point of crgo lamination.
Explain what is use of lockout relay in ht voltage?
any body,pls tell me how to done relay coordination ? how to coordinate by TCC curve?how to read the tcc curve?
how to check regenerative load in drived motor
How to improve fuel cell in a distribution system?