What is the function of positioner in control valves? does the control valve operate without positioner?
Answers were Sorted based on User's Feedback
Answer / someone
No...valve can only be used as on/off purpose..not for control without positioner.
A positioner is a device put into a valve to ensure that it is at a correct position of opening as per the control signal. An I/P converter only sends the opening/closing request to valve but can not confirm its position.
Positioner senses the valve opening through a position feedback link connected to valve stem which is its input signal. I/P converter output is its setpoint input. The difference between these two is the error signal based on which the positioner positions the valve to correct position to reduce error to zero. Hence positioner is nothing but a pneumatic feedback controller. Controlled external supply air to positioner provides power to positioner to position a valve. Also positioner is used in a valve when valve operating signal range is different from I/P converter output range.
In recent days software configurable digital positioner are being used in valves which do not require I/P converter and has many features like advanced valve diagnostics, partial stroke testing, remote communication etc.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / jagan kumar
Positioner is used to give the feedback about the position of control value. ie: how much valve has been opened eg: 74%. Obiviously control value work with out positioner
Is This Answer Correct ? | 0 Yes | 5 No |
Answer / jagan kumar
Positioner in control value is used to provide feedback about the position of the value. ie: How much value is opened eg: 74%. control value can be operated without the positioner.
Is This Answer Correct ? | 0 Yes | 6 No |
HOW TO DO PERFECT CALIBRATION OF DIFFERENTIAL PRESSURE TRANSMITTER FOR CLOSE VESSEL TANK LEVEL PURPOSE ???? AND HOW TO MAKE ZERO PRESSURE ?? Rosemount 2051 Pressure Transmitter with HART® Revision 5 and 7 Selectable Protocol BIENG USED !! HOW TO CALIBRATE FIELD SIDE DPT WITH THE HELP OF SPAN & ZERO PUSH BUTTONS ??
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
how many maximum enter 2mm Dia solid cylindrical pipe into 8mm Dia hollow cylindrical pipe. give answer with calculation.
why the steam drum and deaerator level transmitter range is in negative MMWC to zero
3 Answers Emerson, Jindal, JKPM,
What is input and output of plc & dcs
Speedtronic system .
what are the documentation and instrument identification system used to identify the correct device to be calibrated? name atleast three.
what do you know about Foundation Fieldbus?
what is the role of proportional in process control?
How to calibrate vertex flow meter? How to calibrate mass flow meter?
how to callibrate a new i/p converter
how to overhaul control valves.what are the proper procedures.