What is the function of positioner in control valves? does the control valve operate without positioner?
Answers were Sorted based on User's Feedback
Answer / someone
No...valve can only be used as on/off purpose..not for control without positioner.
A positioner is a device put into a valve to ensure that it is at a correct position of opening as per the control signal. An I/P converter only sends the opening/closing request to valve but can not confirm its position.
Positioner senses the valve opening through a position feedback link connected to valve stem which is its input signal. I/P converter output is its setpoint input. The difference between these two is the error signal based on which the positioner positions the valve to correct position to reduce error to zero. Hence positioner is nothing but a pneumatic feedback controller. Controlled external supply air to positioner provides power to positioner to position a valve. Also positioner is used in a valve when valve operating signal range is different from I/P converter output range.
In recent days software configurable digital positioner are being used in valves which do not require I/P converter and has many features like advanced valve diagnostics, partial stroke testing, remote communication etc.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / jagan kumar
Positioner is used to give the feedback about the position of control value. ie: how much valve has been opened eg: 74%. Obiviously control value work with out positioner
| Is This Answer Correct ? | 0 Yes | 5 No |
Answer / jagan kumar
Positioner in control value is used to provide feedback about the position of the value. ie: How much value is opened eg: 74%. control value can be operated without the positioner.
| Is This Answer Correct ? | 0 Yes | 6 No |
can u guys tell me why we are using sheild in junction bos wiring ~! ?
why is an oxygen sensor used in a boiler stack
What is the use of each wire in three wire RTD
sir,would you please send me the Hindustan petroleum corporation limited papers(HPCL).my e-mail ID is ujjwal_sharma1983@yahoo.com
what is the importance of CV in the control valves? how it is calculated?
which type inter lock use in petrochemical refinery,and oil & gas?
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
Positioner usage.
what is plc communication?
PLEASE PROVIDE SAMPLES OF CHEVRON SKILL TESTS
What is difference between loop and zone ?
Why DP transmitters are subjected to high static pressure test of 100 bar. Though they will be used for very small pressure range
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)