Why DP transmitters are subjected to high static pressure
test of 100 bar. Though they will be used for very small
pressure range
Answers were Sorted based on User's Feedback
Answer / hiren
dp transmitter is used to measure DP but the pressure
applied across diaphargm is actual process pressure. so if
any one get fail then transmitter should not fail.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / komal
Static Pressure is done on DP transmitter because of check
if the transmitter can withstand the static pressure acting
due to Line Pressure when in process. The Line pressure can
be 100 bar but the DP that is measured on transmiter can be
as small as 1000 MM H2O.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / mhakave rajesh
it's span of measurement may be less eg 0- 5 bar,but
pressure acting on single side either of hp or lp (i.e.
process side pressure) may be high, so to check zero of tx
at such operating pressure it is........ so and so.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / b.s.m.raju
This is DP transmeter high static preesure of 100 bar.
Small range will be used 10 mbar. but span range very low
Accuracy will be poor.
| Is This Answer Correct ? | 1 Yes | 2 No |
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
what is the advantage of submersible level transmitter compare to ultrasonic level transmitter?
Identification of control valve parts.
0 Answers CCIE, Oil and Gas Jobs,
Why Bently Nevada use negative voltage for vibration probes?
Foe selecting control valve if i have the min,normal & max data of flow rate,inlet pressure& outlet pressure,inlet tem.&density than how can i assure that these data are correct,pl. let me know if therew there is any method to check it.& also how we assure that the Cv we get from this data is suitable for valve for controlling require flow.
In control valve there are two type of valve seat we can use metal to metal seat & soft seat.On this valve seat i have following doubt. 1)I have never seen practically the internal assembly of valve so my doubt is that basically weather the seat is soft seat or metal its basic MOC is same as valve body(SS or CS) only in soft seat we are using PTFE ring & place on valve seat & in metal this PTFE ring is not threr am i correct??????? 2)what are the common general rule for using metal to metal seat & soft seat,means its depend on process parameter like liquid,gas, steam & on valve leakage class.
Why is the orifice tab provided?
How do bending tubing provide better measurement than using tubing fittings such as elbows?
pls suggest suitable MOC of diaphragm for pressure measurement of UREA grade solution service fluid.
what are the different types of terminal lugs used for wiring termination?
how manys ways dp transmitter can be calibrated having range of -150 to 400mmwc,what side pressure u will apply?
what is difference between PLC and DCS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)