why we use 4-20 mA to do calibration of the instruments.why
we cant use 0-20 mA?
Answers were Sorted based on User's Feedback
Answer / kashif mahmood
1) This is called the live zero or elevated zero concept.
It makes us differentiate between the signal failure and
the zero reading of the transmitter. Let's say, LRV=0 mA
and the instrument cable is cut. How can somebody ascertain
that this is process zero(LRV) and not the cable fault.
whereas if LRV = 4mA and the cable is cut, the current
through the loop would be 0mA and one can find out that
this is the cable fault.
2) its the lowest linear possible range with minimum power
consumption.
| Is This Answer Correct ? | 122 Yes | 8 No |
Answer / zainuddin
1.We use 4-20mA is enough weak to ignite spark to prevent
fire. so these method is designed for safety.
2.There are several types to send the signal that
standardized in current(4-20mA), voltage(1-5v) and in
pneumatic (3-15psi 0r 0.2-1 bar). That means, u determine
how u were sending the signal to operate your process. but
here the best to sent the signal is in current(4-20mA).
3.24V is min. supply that transmitter to operate. if u put
supply more than that as long as not over the transmitter
supply range, u still get the same output 4-20mA, but the
voltage is changed. the change of voltage not effect your
process because you used current signal to operate your
process. Usually engineering will use current
rather than voltage because current not reduce at the long
distance to sent the signal. if u use voltage (1-5v) you
are facing with reducing signal(voltage) in certain
distance. however voltage that better to use is only 1-
5v(enough weak to ignite spark).
so here u should have a calculation how to produce signal
1-5V.(calculation can see at previous answers).
it more complicated than current not depend to supply(
either 24V 30V or 40V) & resistance( either 250ohm, 500ohm
or 700ohm) as long as you not reach over than transmitter
manufacturer range, because the transmitter is converter,
that convert standard signal to 4-20mA.
4.so why transmitter has supply range? this is because when
surging happens that the supply is going to transmitter
is still under transmitter supply range to reduce or
minimize transmitter going burned. so that means,
transmitter can operate at any supply voltage as long as
under supply range. it also can protect your process
immediately going shutdown.
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / rathina
Normally we say Live Zero concept. means transmitter shows
0 means due to powerloss or process value loss.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / ramu
For electronic Instruments operates with 24V(DC),will give
output 4-20MA and pnuematic Instruments operates with 20PSI
will output 3-15PSI.These instruments circuits are arranged
in such a manner that the out put should be as mentioned
above because you will get LENIERITY only in these
ranges.If you take 5-22 MA, you will not get lenier output
( 0%-4MA,25%-8MA,50%-12MA,75%-16MA and100%-20MA)
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / seshu
if we use 0 to 20ma, if any case cable was damaged then it
gives 0ma signal. so we r using 4 to20ma
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / sathish r
Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V
.004 A x 250 ohms = 1 V
.02 A x 250 ohms = 5 V
if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.
| Is This Answer Correct ? | 9 Yes | 19 No |
Answer / naresh yadav
Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V
.04 A x 250 ohms = 1 V
.2 A x 250 ohms = 5 V
if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.
| Is This Answer Correct ? | 21 Yes | 35 No |
what is the difference between RS 232,RS 485,RS 422, how they different from each other
What is critcal speed. what is resonant frequency. why we want to cross crtcal speed on higher RPM (early).
Why Bently Nevada use negative voltage for vibration probes?
how to check the leak in thermowells
How is flow measured in square root?
1)why we are using mostly Ultrasonic Flow meters to measure flow, rather than Radar waves? 2)why we are using Ultrasonic waves and Radar waves to measure the Level?
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????
What are the materials use for COntrol Valve body?
1 Answers KNPC, Qatar Petroleums,
Dear sir I am MD.zafar eqbal. I have taken this id from allinterwiev .com I have qustion if you dont mind. 1.what is the maximum operating temprature in instrumentation. 2. I want know about viberation i mean wahat types of sensor used in viberation And what types of trabsmitter used.and hiw to control it and wher is used of viberation transmitter and finally how to control it and what types of fault come. Sorry for disturbing you. I know you have no reason for help me. Because you dont know about me.but i request you please help me these question are very usefull for my feauture.plz sir Thanking you. Sent from Yahoo! Mail on Android
WHAT IS THE MASS FLOW FLOW METER
can we use flow transmitter instead of level transmitter?
Tyes of interface level measurement and how to use that technique for interface level measurement,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)