Answer / kashif mahmood
1) This is called the live zero or elevated zero concept.
It makes us differentiate between the signal failure and
the zero reading of the transmitter. Let's say, LRV=0 mA
and the instrument cable is cut. How can somebody ascertain
that this is process zero(LRV) and not the cable fault.
whereas if LRV = 4mA and the cable is cut, the current
through the loop would be 0mA and one can find out that
this is the cable fault.
2) its the lowest linear possible range with minimum power
consumption.
| Is This Answer Correct ? | 122 Yes | 8 No |
Answer / zainuddin
1.We use 4-20mA is enough weak to ignite spark to prevent
fire. so these method is designed for safety.
2.There are several types to send the signal that
standardized in current(4-20mA), voltage(1-5v) and in
pneumatic (3-15psi 0r 0.2-1 bar). That means, u determine
how u were sending the signal to operate your process. but
here the best to sent the signal is in current(4-20mA).
3.24V is min. supply that transmitter to operate. if u put
supply more than that as long as not over the transmitter
supply range, u still get the same output 4-20mA, but the
voltage is changed. the change of voltage not effect your
process because you used current signal to operate your
process. Usually engineering will use current
rather than voltage because current not reduce at the long
distance to sent the signal. if u use voltage (1-5v) you
are facing with reducing signal(voltage) in certain
distance. however voltage that better to use is only 1-
5v(enough weak to ignite spark).
so here u should have a calculation how to produce signal
1-5V.(calculation can see at previous answers).
it more complicated than current not depend to supply(
either 24V 30V or 40V) & resistance( either 250ohm, 500ohm
or 700ohm) as long as you not reach over than transmitter
manufacturer range, because the transmitter is converter,
that convert standard signal to 4-20mA.
4.so why transmitter has supply range? this is because when
surging happens that the supply is going to transmitter
is still under transmitter supply range to reduce or
minimize transmitter going burned. so that means,
transmitter can operate at any supply voltage as long as
under supply range. it also can protect your process
immediately going shutdown.
| Is This Answer Correct ? | 16 Yes | 7 No |
Answer / rathina
Normally we say Live Zero concept. means transmitter shows
0 means due to powerloss or process value loss.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / ramu
For electronic Instruments operates with 24V(DC),will give
output 4-20MA and pnuematic Instruments operates with 20PSI
will output 3-15PSI.These instruments circuits are arranged
in such a manner that the out put should be as mentioned
above because you will get LENIERITY only in these
ranges.If you take 5-22 MA, you will not get lenier output
( 0%-4MA,25%-8MA,50%-12MA,75%-16MA and100%-20MA)
| Is This Answer Correct ? | 6 Yes | 3 No |
Answer / seshu
if we use 0 to 20ma, if any case cable was damaged then it
gives 0ma signal. so we r using 4 to20ma
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / sathish r
Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V
.004 A x 250 ohms = 1 V
.02 A x 250 ohms = 5 V
if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.
| Is This Answer Correct ? | 9 Yes | 19 No |
Answer / naresh yadav
Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V
.04 A x 250 ohms = 1 V
.2 A x 250 ohms = 5 V
if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.
| Is This Answer Correct ? | 21 Yes | 35 No |
Which are all the commonly used Bordon tubes in the pressure gauges. Do any one use ASTM A 312 tubes for this purpose?
how can leve transmetter calibate in feild .and also put cv and flow plz .....
how to turbine speed measurement?
0 Answers Jindal Steel and Power,
Identify and use the ANSI/ISA-S5.1 consensus industrial standard process symbols.
in i/o panel for digital ouput(do) how much power(in volts) we must give?
how many types of sensor in instrumentation
why t/c is connected parallel and what is the purpose of it
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
What is the difference between ff transmitter and non ff transmitter
what is difference between positioner and position transmitter in control valve
what are procedure of sox-nox calibration
we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)