why we use 4-20 mA to do calibration of the instruments.why
we cant use 0-20 mA?

Answers were Sorted based on User's Feedback



why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / kashif mahmood

1) This is called the live zero or elevated zero concept.
It makes us differentiate between the signal failure and
the zero reading of the transmitter. Let's say, LRV=0 mA
and the instrument cable is cut. How can somebody ascertain
that this is process zero(LRV) and not the cable fault.
whereas if LRV = 4mA and the cable is cut, the current
through the loop would be 0mA and one can find out that
this is the cable fault.

2) its the lowest linear possible range with minimum power
consumption.

Is This Answer Correct ?    122 Yes 8 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / zainuddin

1.We use 4-20mA is enough weak to ignite spark to prevent
fire. so these method is designed for safety.

2.There are several types to send the signal that
standardized in current(4-20mA), voltage(1-5v) and in
pneumatic (3-15psi 0r 0.2-1 bar). That means, u determine
how u were sending the signal to operate your process. but
here the best to sent the signal is in current(4-20mA).

3.24V is min. supply that transmitter to operate. if u put
supply more than that as long as not over the transmitter
supply range, u still get the same output 4-20mA, but the
voltage is changed. the change of voltage not effect your
process because you used current signal to operate your
process. Usually engineering will use current
rather than voltage because current not reduce at the long
distance to sent the signal. if u use voltage (1-5v) you
are facing with reducing signal(voltage) in certain
distance. however voltage that better to use is only 1-
5v(enough weak to ignite spark).
so here u should have a calculation how to produce signal
1-5V.(calculation can see at previous answers).
it more complicated than current not depend to supply(
either 24V 30V or 40V) & resistance( either 250ohm, 500ohm
or 700ohm) as long as you not reach over than transmitter
manufacturer range, because the transmitter is converter,
that convert standard signal to 4-20mA.

4.so why transmitter has supply range? this is because when
surging happens that the supply is going to transmitter
is still under transmitter supply range to reduce or
minimize transmitter going burned. so that means,
transmitter can operate at any supply voltage as long as
under supply range. it also can protect your process
immediately going shutdown.

Is This Answer Correct ?    16 Yes 7 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / rathina

Normally we say Live Zero concept. means transmitter shows
0 means due to powerloss or process value loss.

Is This Answer Correct ?    7 Yes 0 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / ramu

For electronic Instruments operates with 24V(DC),will give
output 4-20MA and pnuematic Instruments operates with 20PSI
will output 3-15PSI.These instruments circuits are arranged
in such a manner that the out put should be as mentioned
above because you will get LENIERITY only in these
ranges.If you take 5-22 MA, you will not get lenier output
( 0%-4MA,25%-8MA,50%-12MA,75%-16MA and100%-20MA)

Is This Answer Correct ?    6 Yes 3 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / seshu

if we use 0 to 20ma, if any case cable was damaged then it
gives 0ma signal. so we r using 4 to20ma

Is This Answer Correct ?    7 Yes 5 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / kenechi

Yes

Is This Answer Correct ?    1 Yes 1 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / sathish r

Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V

.004 A x 250 ohms = 1 V
.02 A x 250 ohms = 5 V

if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.

Is This Answer Correct ?    9 Yes 19 No

why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA? ..

Answer / naresh yadav

Module require 1-5 v for further processing thats why we
use 4 - 20 mA because with 250 ohms resistance we can
easily convert 4 - 20 mA into 1 - 5 V

.04 A x 250 ohms = 1 V
.2 A x 250 ohms = 5 V

if we use 0 - 20 mA it converts 0 - 5 v but we required 1 -
5 v for further processing in module.

Is This Answer Correct ?    21 Yes 35 No

Post New Answer

More Instrumentation Interview Questions

The pressure class rating (such as 150 lb, 300 lb, etc.) of a line appears in the form of ________________ in the Line Number (or Line Designation) on a P&ID

1 Answers  


What is use of condensate pot

5 Answers   Alstom, Petrocil, Samsung,


flow transmitter formula?

0 Answers   BEMCO, Siemens, Yokogawa,


how does we do bench calibration of a differential transmitter.

1 Answers  


If I installed wrong directions orifice plate then what showing value d.p transmitter?

2 Answers   Forbes, STS,






how to measure level under ground tank ? which type of transmitter very accuracy ?

3 Answers   Biocon,


Can we place a Control Panel in Hazardous area Group IIC ? If 'yes' then is there any approval required? If 'yes' then there is any specific IP rating or any standard required? If 'Yes' What is MOC of control panel?

2 Answers  


what is function of sensor, and how is it work , explain with difination

0 Answers   Bapco Bahrain Petroleum Company,


What is Burnout feature in a recorder?

1 Answers   CCIE,


i want to know for good instrument engineer or success how many software knowledage required & from which university

0 Answers  


what effects a surging can produce in the compressor

0 Answers   Nemat,


how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?

0 Answers   Chevron Phillips,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)