What are the different protection systems used to protect
the transformer internally and externally?
Answers were Sorted based on User's Feedback
Answer / sewagudde
tx protection includes:
buccholz relay
oil and winding temperature relay
pressure relief valve
restricted earth fault protection
differential protection
tx earthing
Is This Answer Correct ? | 46 Yes | 2 No |
1) Differential Protection
2) Winding Temp
3) oil Temp
4) Under Voltage
5) Under Frequncy Protection for Higher Range of Power
Transformers
6) Bucholz Protection
7) Pressure reilef Valve
8) Restricted Earth Fault Protection
9) Master Trip (ie Inter Trip )Conected to isolate X'mer
Brom Both Ends
Is This Answer Correct ? | 24 Yes | 4 No |
Answer / remus de jesus
In our design, the common protection would be:
1. Bucholz Relay (96) - initiates transformer differential
lockout
2. Pressure Relief (63) - initiates transformer
differential lockout
3. Winding Temperature (26W) - initiates first a timer set
between 0 to 30 minutes, and after a pre-determined time
will initiate differential lockout
4. Oil Temperature (26Q) - initiates a timer set between 0
to 30 minutes, and after a pre-determined time will
initiate differential lockout
5. Sudden Pressure - initiates transformer differential
lockout
6. Transformer Overcurrent (50/51/50N/51N) - initiates
tripping of low side breaker
7. Ground Protection/Ground Overcurrent Relay (51G) - the
connected relay in the neutral of the wye winding is used
generally to protect bank circuit from ground faults
Fire fighting protection protects transformer from external
fires. But if fire is caused internally, this mechanism
provides no protection of the transformer at all.
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / venkat iyer
1) Differential Protection
2) Winding Temp
3) oil Temp
4) Under Voltage and over voltage
5) Under Frequncy Protection for Higher Range of Power
Transformers
6) Bucholz Relay Protection for oil cooled transformers (to
detect incipient fault)
7) Pressure reilef Valve for oil cooled transformers
8) Restricted Earth Fault Protection
9) Overload, short circuit and earth fault protection
10) Protection against fire in case of oil cooled
transformers
11) directional protection
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / dinesh kumar
1.Gas Operated Relay ( GOR )/Bucallas Relay
2.Magnetic Oil level Guage
3.Winding level Indicator
4.Oil Level indicator
5.oil Pressure indicator
Is This Answer Correct ? | 10 Yes | 5 No |
Answer / minal
one of the protection systems used in the transformer is
Gas operated Bucholz relay.
The transformer is filled with oil. On passing current
through it, gas bubbles are formed inside it.After the
formation of gases, immediately the relay gets operated &
it will sense the gas which gets build inside the
transformer. These gases are harmful and which switchoff
the transformer. This relay sense the gas & trip off the
transformer before a fault is occured
Is This Answer Correct ? | 12 Yes | 7 No |
Answer / hassina bibi
1.Buchholz relay
2.Lightning arrester
3.Differential protecton
4.Sudden pressure relay
5.Pressure relief relay
6.Overcurrent relay
7.Overfluxing relay
8.Overvoltage protection
9.Restricted earth fault relay
10.HRC fuses (Small distributon transformer)
11.Horn gaps
12.Thermal Overload relay
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / remus de jesus
And another thing....I thought I have already said it...
8. Transformer Differential Protection (87T) - initiates
transformer differential lockout
Is This Answer Correct ? | 4 Yes | 2 No |
Draw an S.L.D of the main panel for a hospital, showing meter position. Essential loads are: 1) Equipment load 100 KW 2) Critical load 500 KW 3) Life AID Safety load 400 KW 4) NON-Essential load 200 KW 5) Other service loads 200 KW Calculate and suggest the size of the transformer, size of main cable, capacitor bank, and calculate the capacity of an emergency load having above first three mentioned loads is supplied by an emergency generator.
Hi.. I am a BE GRaduate in E&E. I have 8.5 Experience in Tendering & Estimation field. I have done SAP SD course few years back. But due to some reason i failed to get job in that field and continued my own field. Now I am thinking of changing into SAP seriously. How should i go ahead???
FRIENDS, I am doing DEEE (part time)final year. Give me some ideas for project
to calculate voltage drop of cable which current we consider that means full load current or panel size?
how we select HRC FUSE ?
how one can know the charging time, discharging time of a 12 VDC battery ? If i have a battery of 12 VDC , 4.0 AH , how long will it take to charge from a charger (power supply) of input 220 V , Output 15 V and output current of 3000 mA and how long will it take to discharge whether using or not ? How much backup will it give ?
why trip circuit supervision is taking through breaker contact? what happen if takendirectly?
In constant power region of 3-phase IM torque-speed characteristics, if frequency increases slip A does not alter B decreases C increases D none of above
What is the rating of circuit breaker needed for 300 KVA load in 33 KV supply line in a transformer of 33 KV / 415 Volt ?
what is the use of conservator in a transformer?
6 Answers L&T, TATA, Tata Motors,
What is function of inverter? and who it's operate & what are controlling devices are used?
How to select the earthing transformer,for DELTA TO DELTA TRANSFORMER OR ALTERNATOR SIDE.Pls post your answers and calculation.