What are the different protection systems used to protect
the transformer internally and externally?
Answers were Sorted based on User's Feedback
Answer / manoj kumar sankaralingam
i)Differential protection
ii)Restricted earth fault protection
iii)Buchholz relay
iv)Oil temperature indicator
v)Winding temperature indicator
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / karthikeyan
Bucholz relay
under voltage relay
over current relay
inverse time current over relay
pressure relay
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / viren89desai@yahoo.co.in
https://library.e.abb.com/public/4381d7d675f760cdc12575550081d599/AG03-5005E_en_Power_transformer_protection.pdf
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vinod g
Transformer protection
1) protection provided in the transformer are
A) buchholz relay for both main and oltc (ansi no 63)(alarm and trip)
B) winding temperature (wti) 49(alarm and trip)
C) oil temperature (oti) 49 (alarm and trip)
D) explosion vent or prv
e) Magnetic oil level gauge for alarm
f) Fire protection (Mulsifire system)
g) Lightning Arrester provided in both HV and LV
2) High Voltage side Protection
a) differential protection 87 (operate when fault occurs between HT CT and LV CT)
b) REF restricted earth fault 64 for winding protection
c) over flux for higher rating transformer
d) directional over current towards the source side, operate when fault feeding from LV during coupled with other transformer
NOTE: Master trip 86 relay is provided as the above relays are having less current rating output contacts, can not provide sufficient current huge trip coil circuit breaker. also 86 is provided with manual reset
3) Low voltage side Protection
Instantaneous and time delay over current 50
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / avinash
Over current and earth fault Protection relay
Differential Protection relay
Restricted earth fault relay
oil temperature alarm & trip
Winding Temperature & trip
oil Level trip
buchhloz relay
oil surge relay
pressure relief device
HT breaker
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / imdad husen
IN TRANSFORMER PROTECTION IF HIGH INTERNAL FAULT OCCUR BETWEEN L.V.C.T.AND H.V.C.T. THEN DIFFERENTIAL RELAY SHOULD BE ORATED AND EXTERNAL FAULT OCCUR DIFFERENTIAL RELAY SHOULD NOT ORATED BECAUSE OF ZERO SEQUENCES CURRENT IS ABSENT
IN TRANSFORMER PROTECTION IF EXTERNAL FAULT OCCUR RESTRICTED EARTH FAULT RELAY SHOULD BE OPARTED
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the significance of cabability curve of alternator
why indian power system having 11.22,33 KV ???
Can someone tell me how to calculate the size of a power cable? What are the factors involved in cable sizing?
Give accurate definitions for these electric terms: Inductor Inductance Inductive Induction Reactance Reactive Esam Baraka ٢١ ساعة
wheather the size of windings in motor and generator are the same
what is load cell
What is the resistance of human body from head to toe?
10 Answers Bhel, Getco, Infosys,
why transformer core is eathed?
3Cx240 & 3Cx300 sqmm Al. cable from lv side. What is the calculation for this cable??
Which colour of earthing wire
If an induction motor is restarted before its rotor stop rotating, then what will be the amount of current drawn? Is this current will be the same as motor starting current?
Operation of isolators.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)