What are the different protection systems used to protect
the transformer internally and externally?

Answer Posted / hassina bibi

1.Buchholz relay
2.Lightning arrester
3.Differential protecton
4.Sudden pressure relay
5.Pressure relief relay
6.Overcurrent relay
7.Overfluxing relay
8.Overvoltage protection
9.Restricted earth fault relay
10.HRC fuses (Small distributon transformer)
11.Horn gaps
12.Thermal Overload relay

Is This Answer Correct ?    7 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

If any one's require of phoenix contact like( relay , termilnal block , surge protection device ) , product please contect me 09878206357 chetan verma

1627


What is the limitation of kirchoffs law?

636


What are the components of feedback control system?

610


How do i right a ladder diagram that has 1 actuator that performs a full stroke followed by a half stroke

1613


What is the difference between cylindrical-type and sandwich-type winding?

936






what are the available sizes of pin type terminal lugs in the market today?

1407


How to calculate cable size by using load.?? Any formula...

893


how to calculate the lightning arrester conductor @ no of earth pits required

1592


Would you recommend to replace all oil filled cables with xlpe cable for hv transmission with the current technolgy for xlpe cable?

1055


what does mean of RCT and STR in diffrential CT?

3756


How do we calculate the resistance per metre of single core aluminium stranded cable 19*3.25mm sheathed in pvc,at 15 deg C temperature?

1930


What is mathematical model of a control system?

637


i need to give section engineer (electrical engineer) for RRB. Please suggest some book

1444


what happen ehen synchronisation is done at below rated speed

1605


(In MEP services) HVAC in AC Plant room what else can we provide if the chiller is not considered?

1577