What are the different protection systems used to protect
the transformer internally and externally?

Answer Posted / venkat iyer

1) Differential Protection
2) Winding Temp
3) oil Temp
4) Under Voltage and over voltage
5) Under Frequncy Protection for Higher Range of Power
Transformers
6) Bucholz Relay Protection for oil cooled transformers (to
detect incipient fault)
7) Pressure reilef Valve for oil cooled transformers
8) Restricted Earth Fault Protection
9) Overload, short circuit and earth fault protection
10) Protection against fire in case of oil cooled
transformers
11) directional protection

Is This Answer Correct ?    12 Yes 2 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

What is reactive power and where it is used.

1181


What is cable tray, its type, and its support?

657


How to connect the chemical earthing and complete process tell me plz

1382


The 3 phase Delta connection RB=440V, BY=350V,.......* is Line to Line voltage RY= ? And Formula....?

1149


What is the universal motor?

636






What is Scheme Test of High Voltage Switchgear. Which tests it includes.

1886


What is a signal flow graph?

633


before synchronizing an alternator,power factor is leading ,why?

1005


WHTA IS LIMT OF LEAKGE CURRENT OF 11 KV 1 CORE 1000SQ.MM. XLPE CABLE.LOAD ON CABLE IS AROUND 600AMP .LENGTH 500 MTRS.

1652


Can we use both Electrical & mechanical interlock between tow breakers? if yes how, please explain

960


what is meant by 2 within a star in a voltmeter dial?

1501


1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to confirm its base capacity?

1539


How to calculate cable size in HT AND LT

1498


What are locations arc protection relay is fixed.

1345


Two liquids hot and cold in two vessels are there and an metal bar acts as a conductor of heat between the two vessels. what happens then. what happens after 24 hrs?

1698