Answer / k.prakashchandra
In-built protection is for currents exceeding the rated
current of the breaker,which is usually higher than that of
your requirement.Further, you can not alter this unless you
replace the cts.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / k.prakashchandra
In other words ,if the in-built CT does not meet your
requirements ,you have to use external ones.
| Is This Answer Correct ? | 0 Yes | 1 No |
why fuse not recomended to neutral
what is the reason for balance of voltage in magnetic balance test?
why burdens of VTs is more than CTs?
How to select busbar?
What are the relays in ACB and VCB
How much amps carry in single phase R-phase,in D63A 4-pole MCB
374kvar capacitor bank connected across 600kw,6.6kv motor.what will happen if motor run at 50% , whether full kvar applied or half?
Can we check ELCB constantly from R1 to R8 phase in 1 no DB?
1)Why V cross Arm is used in transmission lines? 2)Why H cross Arm are not used in single poles?
why do we have 230v a.c. as general voltage for domestic supply rather than others?
If DG runing time neutral is disconnected what will be the effect in Engine and Electricial panel.
Give the selection criteria of a 3 Phase transformer for industrial purposes ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)