Hai friends I have dought for O2 analyser how to working in boiler area. And what is the basic principles
Answers were Sorted based on User's Feedback
Answer / rambalaji
1. zirconia oxygen analyzers determine oxygen concentration using the conductivity of a zirconia ceramic cell. Zirconia ceramic cells only allow oxygen ions to pass through at high temperatures (750oC). With reference gas on one side and sample gas on the other, oxygen ions move from the side with the highest concentration of oxygen to that with the lowest concentration. The movement of ions generates an EMF (Electro Motive Force) which can be measured to determine the oxygen content
2. The sensor does not actually measure oxygen concentration, but rather the difference between the amount of oxygen in the flue gas and the amount of oxygen in the air. Rich mixture causes an oxygen demand. this demand Causes high voltage to build up due to transportation of oxygen ions through the sensor layer. Lean mixture causes low voltage since there is oxygen Excess. Sensor working in Nernst Principle
In flue gas side O2 is low : High Voltage
In flue gas side O2 is high : Low Voltage
High Concentration : O2 + 4 e 2O2 -
Low Concentration : 2O2 - O2 + 4 e
0% O2 = 0.82 mv
5% O2 = 0.40 mv
21% O2 = 0 mv
Is This Answer Correct ? | 4 Yes | 0 No |
. When temperature increases the content of oxygen decreases.- principle.
Reference gas(span gas) instrument air 21% O2.
1% gas should provide from cylinder for cal purpose.
Is This Answer Correct ? | 3 Yes | 1 No |
diff between neutral ,ground,phase , earthing and shielding?
what is different between modbus and serial link? please could anybody give right answer.
For what Wake Frequency Calculation is used?
What is the difference between sdv and bdv ?
We have a Yokogawa Micro-XL DCS, which is having around 300 I/O, but whenever there is any wire gets grounded in field, the 24v supply to all loops gets dipped & all the indications at DCS goes to IOP(shows input open), at present we have fixed 500mA fuses in all the lines but which does not working. Does it required to replace with lower amps fuse, then how much or is there any other solution for this.
Why do we use 24V DC supply in instrumentation? What are its merits and demerits??
while am calibrating Drager polytron 2IR flame gas detector occured non zero status.how can i get zero status?
What is DDC-MIS?
in pressure gauge inside why we are using the glasarin oil?
what is difference between OP AMP and differential amplifier?
What types of thermocuple are mostly used?
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .