Answer / haridass
In normal running plant the ESDVs will not be operated
unless there is an emergency situation, it happens rarely.
Sometime those valves will get struck in open position and
it will not help the situation to protect the plant.
So to avoid this kind of problem, the PARTIAL STROKE
TESTING (PST) system is applied. Periodically, the ESDV
will be closed 20% from full open to close and immediately
open fully, which will not affect the process flow. This
movement makes the valve free from struck-up.
This PST function takes place only when the valve is full
open. During the valve close PST FAIL alarm will be
occured. and recorded in the event summary.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yasir & farhan
we give nearst 70 psi so just we that esdis fully open or
close
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kyle condran
So you know your actuator works without fully closing you esd valve, as this is not a good idea unless you want to upset your process.
| Is This Answer Correct ? | 0 Yes | 0 No |
I HAVE GOT TYPICAL PROBLEM WITH THE TEMP.INDICATION. THE PROBLEM IS THE K-TYPE T/COUPLE OUT PUT IS CONNECTED TO A INDICATOR.THE INDICATION FLUCTUATES SOME TIMES AND SOME TIME IT IS STABLE. WHEN I CHECKED OUT PUT OF T/COUPLE THE MV WILL NOT VARY. WHERE AS INDICATION FLUCTUATES. WHEN I GIVE MV SOURCE TO T/COUPLE EXTENSIONCABLE FROM THE FIELD IT INDICATION IS STABLE. WHEN GIVE MV SORCE TO INDICATOR ITS INDICATION IS STABLE. PLEASE CLARIFY.
how to measure low temperature(<100 dec celsisus) with non condact sensor
What is the syllabus for Instrumentation Engineers, who wish to join the Public Sector Units??
IS THEIR ANY AGEING EFFECT ON FLOW NOZZLE, ORIFICE, MANIFOLD, OR TRANSMITTER ?
Explain pH, Conductivity.
what is loop folder?
1 Answers Bapco Bahrain Petroleum Company, Hyundai,
what is the difference b/w wet leg & dry leg level method
how to change measuring units from mmwc to cubm/h in rosemount air flow transmitter with hart communicator fluke 744
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
in sulfur process what is material of impulse line we use to connect with transmitter ? and does teflon affected by sulfur?
what is the difference between transmitter and smart transmitter ?
what is different between 2,3&4 wire rtd and how much maximum distance using plc to field.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)