HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY
IT IS USED ON ESD ON OFF VALVES?
Answers were Sorted based on User's Feedback
Answer / haridass
In normal running plant the ESDVs will not be operated
unless there is an emergency situation, it happens rarely.
Sometime those valves will get struck in open position and
it will not help the situation to protect the plant.
So to avoid this kind of problem, the PARTIAL STROKE
TESTING (PST) system is applied. Periodically, the ESDV
will be closed 20% from full open to close and immediately
open fully, which will not affect the process flow. This
movement makes the valve free from struck-up.
This PST function takes place only when the valve is full
open. During the valve close PST FAIL alarm will be
occured. and recorded in the event summary.
Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yasir & farhan
we give nearst 70 psi so just we that esdis fully open or
close
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kyle condran
So you know your actuator works without fully closing you esd valve, as this is not a good idea unless you want to upset your process.
Is This Answer Correct ? | 0 Yes | 0 No |
How to calculate 47Liter H2 Gas cyilnder consumtion? Cylinder inlet Pressure is 200bar and Discharge pressure is 6.0bar. Flow is 100ml/min.For the above condition how many days one cylinder can be used?
How to find out turn down ratio of Pressure transmitter?
If I want to buy a pressure switch & 3-way valve for hot water application then witch parameter I should consider.
What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?
How to connect PLC to DCS ?
what is working principle of presure and temperature guage?
Guy's need your support,I want to measure closed tank level which is under vacuum -630mmHg using DP Transmitter, tank fluid density 1.38, Tank height is 7ft
How to work & calculated output of the Derivative action in pid controller (Explain Derivative controller)
defffrence between instruments and instrumentation
what is the difference between transmitter and converters?
any one suggest me how to calculate percentage of air leakage with formula,
What is possitive and negative feedback?