HI FRIENDS IHAVE QUESTION 1.WHAT IS PARTIALSTROKE TEST?WHY
IT IS USED ON ESD ON OFF VALVES?
Answers were Sorted based on User's Feedback
Answer / haridass
In normal running plant the ESDVs will not be operated
unless there is an emergency situation, it happens rarely.
Sometime those valves will get struck in open position and
it will not help the situation to protect the plant.
So to avoid this kind of problem, the PARTIAL STROKE
TESTING (PST) system is applied. Periodically, the ESDV
will be closed 20% from full open to close and immediately
open fully, which will not affect the process flow. This
movement makes the valve free from struck-up.
This PST function takes place only when the valve is full
open. During the valve close PST FAIL alarm will be
occured. and recorded in the event summary.
| Is This Answer Correct ? | 8 Yes | 0 No |
Answer / yasir & farhan
we give nearst 70 psi so just we that esdis fully open or
close
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / kyle condran
So you know your actuator works without fully closing you esd valve, as this is not a good idea unless you want to upset your process.
| Is This Answer Correct ? | 0 Yes | 0 No |
List three types Level Transmitters with their working principles
1 Answers ABB, Bapco Bahrain Petroleum Company,
what is RPI and NUT in controlnet networx. what happen if we are increase the NUT of controlnet networx?
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
Why any transmitter signal is 4-20 mA only Why is started from lower range 4 mA and upper range is 20mA.
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
WHY WE WILL USE 0-24VdC IN ELECTRONIC CIRCUITS AND INSTRUMENTATION TRANSMITTERS?
3 Answers Aban Power, Jindal, JSW, Sugar Factory,
Is there any relation between Artificial Intelligence and Instrumentation?
In oil & gas industries and petrochemical industries, there are classification of zones like zone 0, zone 1, zone 2. Is there any differences in voltages or power supply supplied for the process instruments, control instruments depending on the zones
i have a dp tx range is 5000mmwc. in which calibration i use in a open tank.1.5*3.5*2.5 mtr.for level msmnt. what is the calculation.
What is the out put of pressure switch & electronic pressure transmitter.
5 Answers ADMA OPCO, Al-Barrak,
In close vessel/ drum why we use d.p. transmitter of -ve range i.e. (-)500 to 0 mmwc.
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)