Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


On LPG sphere tank we used LIT for level indication.High
side port is connected to the bottom of the tank while low
side port connected to the top. I would like to know how to
fill the glycerin on its low side with two condensing pot
installed,one from top and the other one for its drain
line.Please I need your expertise...thanks



On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of th..

Answer / sam

Hi there,

This is called a normal wet leg installation. There is no
need to change the HP and LP around when you use a SMART TX.
All SMART Tx can measure in the negative with the same
amount as in the positive. exp: -1600 to +1600mmH2O

Open your manifold vents to atmosphere and do a zero trim,
next close the equalizing valve on the manifold and open HP
line to atmosphere. Fill the LP line until both catch pots
are full and the Glycerin is running out of the top catch
pot into the line going to the top tapping point of the
vessel. At this point let the liquid in the vessel fill the
HP line. Remember to do some draining to make sure there are
no air bubbles. What you need is to have the LP completely
filled with Glycerin and the HP line filled with Vessel
liquid up to the point where the tubing connects to the
vessel(not more). Whatever the transmitter reads now(neg
value)is called an atmospheric zero value(ATM).DO NOT DO A
ZERO TRIM!!
Use this formula to calculate the LRV and the URV

LRV = ATM value + (distance from bottom tapping on the
vessel to 0% point on vessel x the sg of the vessel liquid)
URV = ATM value + (distance from bottom tapping on the
vessel to 100% point on vessel x the sg of the vessel liquid)

LRV and URV UOM must first be in mmH2O if you took these Z/S
measurements in mm. After you install them with the HART you
can change it to whatever UOM you require.

Is This Answer Correct ?    4 Yes 0 No

Post New Answer

More Instrumentation Interview Questions

1.how can calibration temperature transmitter and flow transmitter? 2.

0 Answers   Gulf Jobs,


hey any one got the papers of SAIL and HPCL plz do help me by posting them to my mail ID's naren07_87@yaho.co.in, surenarendra@gmail.com

0 Answers  


what is interface level and how it is calibrate?

0 Answers  


Which type of diaphragm use in costic line, dm water line, natural gas line, oil line?

0 Answers  


What different types of problems do occur while doing the loop checking? and please explain in detail or mail me at kadam.aniket143@gmail.com

1 Answers   Operational Energy Group, Process Control Technologies,


With N nodes and B branches what will have a network ???

0 Answers   BSNL,


why is the sleeve of the cable used for?

2 Answers   Jindal,


how control valve works?

7 Answers   Qatar Airlines,


1. What means HART communicator / where it is used / how to use it? 2. Types of Thermocouples and its temperature ranges / output of thermocouple? 3. Types of RTDs and its temperature ranges / output of RTD? 4. Idea about Temperature Transmitters? 5. Difference between Analog and Digital signals? 6. Difference between “2 wire” and “4 wire” system / instruments? 7. Difference between “Potential” and “Potential free” contact? 8. Types of flow meters / transmitters? 9. Types of level transmitters? 10. Difference between “Power/Control” cable and “Instrument” cable? 11. What means “shield” and “screen” in cables / how it is useful? 12. Draw a schematic of closed loop circuit of flow / level / pressure / temperature? 13. Idea about calibration of Control valve / positioned / I/P? 14. How to bypass a digital/analog signal in PLC/DCS by hardwire and software?

6 Answers   JSL,


can any one tell me when ongc placement test and its forms is available????/ pls tell me if u know

0 Answers  


How to check vortex flow meter is in good condition while we do not having calibration setup?

4 Answers  


who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.

2 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)