why we are using negative range like -750 to 0 mmwc in
closed tank?and what is the reason can you explain clear?
Answers were Sorted based on User's Feedback
Answer / navodit
whenever there is close tank, there is vapour which will
condensate in top taping tubing(LP taping), which will
remain there even after empty tank, that time output
pressure will be in negetive(as HP taping is empty and LP
taping has filled with condensate), as LP line is filled.
so negetive will shove 4 mA at negetive value
| Is This Answer Correct ? | 11 Yes | 0 No |
Answer / varma
In Closed tanks vapour condensates and accumulate in LP impulse line, to eliminate this problem glycol will be filled
in LP impulse line. The positive head pressure which is created by the glycol density and the height of the LP impulse line has to be suppressed. For example LRV and URV are 0 to 750mmh2o, 750mmh20 of positive head pressure to be substrated for each value then u will get the value of LRV and URV as -750 to 0mmh2o.
| Is This Answer Correct ? | 4 Yes | 2 No |
How many mode are in ups?
I have a LT of 10000mmwc range. can i use this LT in 1000mmwc range of tank?? if yes than what happened???
why? Boiler furnesh pressure transmitter mount in boiler top and it's impulse line is in bottom of the boiler. Aneybody kindly tell me this reason.
what is cold loop? difference between hot and cold loop?
During valve sizing from all calculation you got flow coefficient CV 12,than what it means? like for selecting pressure transmitter if your MAWP is 12 bar than you select a capsule of max. 20 bar which cover your mawp 12 in same way for selecting control valve If CV is 12 than how we use it in selecting valve??????
Give an example where you had aproblem on the job, and tell me how you solved the problem. and the finalvoutcome.
why we use the 4-20 mamp signal used for transmitter.
Why some transmitter shows flow in MMWC and some in TPH?
CAN WE CALIBRATE LEVEL TRANSMITTER USING HART COMMUNICATOR WHEN WATER LEVEL IS PRESENT IN THE BOILER SHELL?
What is the maximum distance limit of 4-20mA and 0-10V DC standard signal transmission ?
WHAT IS A SYMPTOM OF FAULT WITH THE SPAN OF AN INSTRUMENT? 1)ZERO-POINT AND 100% ARE CORRECT BUT NOT A MID-RANGE. 2)ZERO-POINT IS CORRECT ,BUT 1005 INPUT IS NOT GIVING 100% OUTPUT. 3)LINEARITY PRBS. 4)1005 O/p IS CORRECT BUT ZEO POINT IS WRONG.
State some of balance principle’ advantages?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)