under which situation or why restricted earth fault protection operates in out side its zone that is external fault
Answers were Sorted based on User's Feedback
Answer / hg
1) if any one ct saturates at through fault current due to
a) high harmonic content of current in through fault current leading to high voltage appearing across secondary and the ct saturates
2) under above scenario if there is no stabilizing resistor/ damage to stabilixing resitor than relay may operate
| Is This Answer Correct ? | 0 Yes | 0 No |
This may happen when bushing neutral ct is used for REF , as it is usually not identical to the line ct s
| Is This Answer Correct ? | 0 Yes | 0 No |
voltage and frequency is equal but synchronisation not complete why?
What vibration parameters are monitored in a directly coupled single cylinder turbine and generator?
How to calculate power press toneage
what is under voltage protection 27
In a thermal power plant ID Fans running with full load but boiler load is only 80 % give reason ?
9 Answers Essar, Prumatech, Tata Power,
our 125 kva DG does not start in AUTO mode works normally in MANUAL mode please give me a solution.....
2. what is meant by exhausthood temp?
explain(why) with circuit for pick up of restricted earth fault protection due to external fault
Where is the pressure reduce valve in the power plant
Why cold water is used for Boiler Hydro test
why HT motor star not grounded?
What is difference between Actual Drum Level and Compensated Drum Level?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)