Why generator is not connecting in delta ..why connecting in star ?
Answers were Sorted based on User's Feedback
Answer / guest
In star connection voltage/phase=line voltage/1.73 and emf induced in generator is directly proportional to number of turns. So in star connection we have to use less number of turns & insulation.star connection is most economical than delta
| Is This Answer Correct ? | 11 Yes | 2 No |
Answer / ajay
Delta have 3rd harmonics which maintain circulating current in closed delta which cause heating effect.
Y connection provide neutral for installing relays and circuit breakers which are connected in per phase manner.
| Is This Answer Correct ? | 7 Yes | 5 No |
Answer / narahari
in delta line voltage=phase voltage,but in star connection line voltage=root3*phase voltage then it gives more voltage than in star
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / nitin khatana
generator are always connected in star to prevent 3rd harmonics circulating current.another reason is in star connection (v line/root 3 =vph) so insulation thickness requirement is less in star in the given space and slot.
| Is This Answer Correct ? | 1 Yes | 0 No |
why do we prefer a 3-phase delta connected load rather than star connected?
Can we step up a 230V supply to 400V using a single phase transformer??
In Siemens S7-300 PLC, what is funtion and funtion block ? What is the difference between them ? When to use function and when to use function block
What is the unit of charge and current?
how to put cable sizing and cable glands size for respective cable & Cable Lug size in a DB sectors???
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
What is Annunciation?
SIR, GIVE ME OPGW SAG CALCULATION FORMULA I AM DAE ELECTRICAL. THANKS
why excitor coil of an alternator can fail
Why the generating station rating is in KW though the rating of generators in KVA?
When testing an earthing connection, we use a 60 or 100 candle bulb with a phase connected direct from supply and the other wire to the new earthing provided.If the bulb glows then the earth is ok.Else earth connection is not Ok. So, why dont we can use all the home appliances taking a single wire from the phase and the return connection to Earth instead of return connection to neutral?
What happen if we have run 415 V,50Hz designed motor at on 480V,60HZ
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)