Why transformer rating in KVA?
and Generator also?
Answers were Sorted based on User's Feedback
Answer / chvnraja
Any device is rated depending on losses of the machine. In a
transformer the losses are iron losses which depends on
voltage and copper losses which depends on current so there
are no losses which depend on power factor hence transformer
is rated in KVA
| Is This Answer Correct ? | 32 Yes | 0 No |
Answer / rahul
In a transformer Losses(I^2R-Iron and Copper Losses)depends
on voltage(Volts) and current(Amps).so the rating wshould
be in KVA
| Is This Answer Correct ? | 29 Yes | 5 No |
Answer / a.muthukumar, vacon
Cu loss of a transformer depends on current and iron loss on voltage. Hence, total transformer loss depends on volt-ampere (VA) and not on phase angle between voltage and current. It is independent of load power factor. That is why rating of transformer is in KVA and not in KW.
| Is This Answer Correct ? | 17 Yes | 1 No |
Answer / nilamanineel@yahoo.com
but nobody did not say about alternator
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / deepak
this is because the KVA rating give active plus reactive
power components and the reactive power is associated with
losses of the machines. KW rating tells about the power
being transfered not the losses associated with the process.
| Is This Answer Correct ? | 3 Yes | 8 No |
Answer / aniket
as the is not known we cannot know the power factor so cant xpress in watts so in kva
| Is This Answer Correct ? | 5 Yes | 14 No |
IF THE OUTPUT OF A 100KVA, 415V GENERATOR IS STEPPED UP TO 11KV WITH A 500KVA TRANSFORMER,CAN THE TRANSFORMER BE LOADED ABOVE THE SOURCE GENERATOR RATING?
what is the principle of singkle phase energy meter?
what is the main parts of DG? how it is working?
how single phase preventer works ?
How much heat will a 2500 KVA transformer will generate ?
If one lamp connect between two phases it will glow or not?
size of condotory fron voltage level
The mechanical angle is electrical angle A always less than B greater than or equal to C equal to D less than or eaual to
why power factor is only cosine angle not sine angle?
What is TVSS Protection???
hello, I need to know exactly what happen in the motor while it is connected to the (star/delta) starter, mechanical and electrical. Thaks for answering
why we commonly use delta star winding in power and distribution transformers
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)