Please let me know when replacing electromechanical
Relays for protection of generators with sr489 multilin
Relay, then there is no need to use 86 master trip relay
Too. I am wondering this multilin relay has no contact to
Stop breaker reclosing as 86 does
The electronic relays do not have heavy duty contacts and they are usually self reset. Tripping relay is required to take high trip currents and they are to be reset . Otherwise the contacts of e- relays will burn out and breaker may close without clearing fault . In addition , a back up EM relay may be required
Is This Answer Correct ? | 0 Yes | 0 No |
what is safety of ups
What is the implications when 600 hp motor is started when the unit is running with Transformer of capacity 1500 KVA and DG set of 1000kva
For backup batteries connection,which method is best? series or parallel ?
What is the maximum breakdown voltage of 11KVA and 66 KVA power line and how it is calculated?
0 Answers Anglo Platinum, Narnarayan Electrical,
can any one explain about when EB supply failed then how the load will transfer onto DG's step by step.
hi can anyone pls tell me the eee interview core questions asked in l&t
why the vfd motor take current high in vfd panel then mcc panel.current in vfd panel=160A in 93%.and mcc panel it shows 130A. (132kw motor)
why high speed tripping relay is used in protection circuit why not normal relay
Which of the following alternatives will be cheaper (1) A 100 h.p AC, 3-phase motor (2) Four motors of 25 h.p each (3) Five motors of 20 h.p each (4) 10 motors of 10 h.p each explain
pls send previous bhel electrical papers
how can 3phase motor speed can be controlled without vvf drive?
In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.