A motor works on 30kw.it is working on 440volts.How much
amper will be Required?
Answers were Sorted based on User's Feedback
Answer / a.bala
Hai Ramya
The formula for I= KW/ 1.732x pf x Applied voltage in kv
So
KW =30
pf=0.8
Applied voltage = 440 v =440/1000=.440
30/ 1.732x0.8x.440=49.2 A
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / dinesh raj
Voltage =440 V
Power Facter (cos@) = 0.8
Power P = 30kW = 30000W
Formula for 3phase power P = sqr(3)*V*I*cos@
So Current I = P/sqr(3)*V*cos@
I = 30000/1.732*440*0.8
So Required amper = 49.2 A
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
30 / Rt3xpfx voltage i KV
30/Rt3 x.8x.440= 49.2 A
Consider starter current 1.2 Time from running current
so 49.2 * 1.2= 59 A
sO you will selecte cable and breaker for 60 A.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sidhu.k
Mr, bala your answer is correct i dont repeat it
again,thank you, i think ramyas dout is clear.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramendra shukla
Hi Dinesh you are correct but you have made a mistake- in
place of sqr(3) there will be root squre(3)
so Power,P = under root(3) VI Cos@
or P = 1.732 VI cos@
then you are correct while your calculation are correct.
| Is This Answer Correct ? | 0 Yes | 2 No |
what happan when ac power transmitted in unity power factor
How the power factor is more in high speed machines
Why birds seating in HT line does not get shock? If person hangs in HT line (single hand or both hands) does he get shock?
Can you explain about TEE protection scheme?
when generator of a power plant is not connected to grid , by increasing the mechanical torque speed of rotor increases but when it's connected to load instead of increase in speed current increases , why?
I AM INTERESTED TO WIND A 3 PHASE MOTOR HOW I CALCULATE TURNS, PITCH,AND WIRE SIZE FROM STATOR DIMENTIONS
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
How you give clearance to a spare feeder.
why voltage drop if we have connected 230 v ac suplly through diode to bulbe we found haft ie 110 voltage drop why it is
When we need up only in o/p 440v, so why we use directly in 11kva in input?
0 Answers Lupin, Medhaj Techno Concept,
What is the comparison between 30mA DP RCCB and 100mA DP RCCB and can replace it against 63A MCB
WHAT WILL BE THE SPEED OF MOTOR IF NO.OF POLES ON STATOR ARE NOT EQUAL TO NO. OF POLES ON ROTOR.???
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)