A motor works on 30kw.it is working on 440volts.How much
amper will be Required?
Answers were Sorted based on User's Feedback
Answer / a.bala
Hai Ramya
The formula for I= KW/ 1.732x pf x Applied voltage in kv
So
KW =30
pf=0.8
Applied voltage = 440 v =440/1000=.440
30/ 1.732x0.8x.440=49.2 A
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / dinesh raj
Voltage =440 V
Power Facter (cos@) = 0.8
Power P = 30kW = 30000W
Formula for 3phase power P = sqr(3)*V*I*cos@
So Current I = P/sqr(3)*V*cos@
I = 30000/1.732*440*0.8
So Required amper = 49.2 A
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / a.bala
30 / Rt3xpfx voltage i KV
30/Rt3 x.8x.440= 49.2 A
Consider starter current 1.2 Time from running current
so 49.2 * 1.2= 59 A
sO you will selecte cable and breaker for 60 A.
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / sidhu.k
Mr, bala your answer is correct i dont repeat it
again,thank you, i think ramyas dout is clear.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / ramendra shukla
Hi Dinesh you are correct but you have made a mistake- in
place of sqr(3) there will be root squre(3)
so Power,P = under root(3) VI Cos@
or P = 1.732 VI cos@
then you are correct while your calculation are correct.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is different between phase and netural
In pakistan appliances work on 220v at 50hz and in us appliances work on 110v at 60hz what is basic theory to explain it
Why earthing is required for diesel tank?
Mathemetical Relation Between KWRH and KWH?
why battery dc voltage become Half when we check with respect to ground for example 120volts + and - terminals and when we check + terminal with Earth thats 60volts why 60volts we can not ground the battery.
what are all the daily preventive maintainance carried out in transformer?
Why is a plain induction motor unsuitable for wide speed control?
Regarding units, for voltage we are denoting Volts as V but in case of current we are not denoting Ampere as A instead as I..Why..? Any technical reason for this..?
what is the difference betn earthed and unearthed cables which is commanly used why?
An ELHNC 80amp 240v 30mA RCD is tripping periodically, every 30 - 180 seconds is it safe to disconnect the protection circuit?
how can we calculate the ratio of caustic soda and water in lrs.
What is MSL designation of a motor and same may be provided in details.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)