Answer / madhu
This kind of starter is required when the motor is required
to run in both forward as well as reverse directions
according to the application.
Power circuit: There is one more power contactor connected
across the power contactor in the power circuit with two of
the phases interchanged to achieve reversal of rotation. The
two contactors are mechanically interlocked to ensure that
both of them do not operate simultaneously. The shorting of
two different phases is avoided through this arrangement.
•
Control circuit: The control circuit obviously consists of
two start push buttons, one for ‘FORWARD START’ and another
for ‘REVERSE START’. Each of them controls the supply to the
respective contactor coils responsible for the supply to the
motor in forward and reverse modes. The stop command is
common for both modes since it is independent of type of
operation. The NC contact of forward contactor is connected
in series with reverse contactor coil and that of reverse
contactor is connected in series with forward contactor
coil. This is the electrical interlock, which ensures that
only one contactor will pick up at a time avoiding any
mal-operation and consequent damage to the feeder and
problems to the dependant processes.
•
Indication circuit: One more Red LED is required to indicate
the ‘Reverse ON’ mode.
One NO contact of the reverse contactor is connected in
series with it.
| Is This Answer Correct ? | 43 Yes | 5 No |
Answer / madhu
RDOL IS NOTHING BUT REVERSIBLE DIRECT ON LINE STARTER.
This kind of starter is required when the motor is required
to run in both forward as well as reverse directions
according to the application.
Power circuit: There is one more power contactor connected
across the power contactor in the power circuit with two of
the phases interchanged to achieve reversal of rotation. The
two contactors are mechanically interlocked to ensure that
both of them do not operate simultaneously. The shorting of
two different phases is avoided through this arrangement.
Control circuit: The control circuit obviously consists of
two start push buttons, one for ‘FORWARD START’ and another
for ‘REVERSE START’. Each of them controls the supply to the
respective contactor coils responsible for the supply to the
motor in forward and reverse modes. The stop command is
common for both modes since it is independent of type of
operation. The NC contact of forward contactor is connected
in series with reverse contactor coil and that of reverse
contactor is connected in series with forward contactor
coil. This is the electrical interlock, which ensures that
only one contactor will pick up at a time avoiding any
mal-operation and consequent damage to the feeder and
problems to the dependant processes.
•
Indication circuit: One more Red LED is required to indicate
the ‘Reverse ON’ mode.
One NO contact of the reverse contactor is connected in
series with it.
| Is This Answer Correct ? | 26 Yes | 6 No |
why tan delta test is carried out in the power transformer? which parameter are measure?
How to calculate the ups battery back up? give the formula.
15 Answers Cushman Wakefield, Ethio Telecom, Exide, MacLellan, Morgan Stanley, TATA,
why induction motor having low power factor at starting time and high at full load.
What is the actual formula for transformer short circuit test? below i given rating of the transformer.. 1000KVA, pri 11KV, Pri amp 56A. %Z 5.95..
what is meaning of 230volts ac 50hzs ac supply is it rms or maximum to getting ac 230v what amount of max voltage they will send
how to check 3phase motor winding with help of multimeter?
What is different between Difnit time and instatous over current relay
What is the maximum advisable distance where it is required to interconnect a 500 KVA 480 V 3 ph transformer and the main panel or MCC ignoring the voltage droop affectation, does it is exist any standard about it?
1. If 8.35%Z means the percentage impedance of 132kV-line from power company, we will like to reconfirm its base capacity.
in 50 mw generator if field is open in full load running condition what happen and for protection which relay used?
Motor,transformers,capacitor tubelight etc....
WHAT IS THE REASON FOR THE GROUND PIN IS BIGGER IN SIZE COMPARING TO OTHER PINS?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)