I find that underground strip-armoiured,4core,LT PVC cables
in an earthed power distribution sytem are occasionly found
in charred condition-with no trace of it except ash. Is
this because of no proper earth connection/continuity
(giving rising to high armour resistance)in the joint
enroute or because of insufficient capability (again due to
high armour resistance)of cable-armour to carry fault
current or due to neglected /unprotected overloading of the
cable or due to high armour currents caused by power thefts
where only phase(s) are unauthorisely tapped & at the point
of poer consumption earth terminal is established by
burring underground a not so good earthing rod (or using an
underground water pipe for the purpose)
Answer / k.prakashchandra
Do not earth both the ends of armour ,only one end is to be
earthed
| Is This Answer Correct ? | 0 Yes | 0 No |
If Polarization index of motor 8.75 at 500volts of medium voltage 4.16 KV motor what this mean winding good or bad pl answer if any reffrence book give me the link
draw single line diagram of UPS
1 Answers Adani Ports, Equate, IBM, SAP Labs, Socomec, TATA,
PRV (Pressure relief valve) Trip with oil splash outside power transformers
What are various impedence in any machine
2 Answers Engineers India Limited, NTPC,
What are the procedures followed for underground cable laying.....???
What are the types of AMF(auto main failure) panel.
Can a dc motor works as a dc generator. If yes , then how?
How to set a Zone 1 distance relay for distribution feeder?
0 Answers Schweitzer Engineering,
i am trying to PSUs/govermeant jobs since last 2 years but still i m not success, plz help me.
when the supply of MSEB is cut off & all the load of the industry is driven on generator at that time the capacitor which is connected in industry for power factor control is switched off why?
Why we are testing a tan delta test in transformer? which purpose conduting that test? and time priode test?
how to calculate the kw, Amps consumed by a capacitor, give me the formula for KVAr into capacitance,KVAr into KW & KVA, Amps
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)