1) How to calculate battery backup for ups as well as solar
with complete formula elaborately......
Answers were Sorted based on User's Feedback
Answer / kuzhali
ups back up time=(AH rating*volt*power factor)/total load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / velmurugan, so/d, barcf, kalpa
Consider the 2 KVA online UPS.
specifications are as follows: output voltage: 230V, Pf:
0.8, Load is 1600W. DC bus voltage is 96V.
Now Total output is = 2000 VA
PF of the load is = 0.8
There fore output in watts = 2000x0.8= 1600W.
Efficiency of the inverter is 80% therefore power input to
the inverter will be = 1600/0.8= 2000W
DC current of the inverter section= Watts / Voltage
Consider the fully charged voltage = 13.5X8=108V
The DC bus voltage
up to which the battery can deliver= 10.5x8=84 Volts.
therefore maximum current drawn by the inverter when battery
is in line = 2000/84=23.8A
Now consider the backup required for the load, i.e 1 hour
back up is required to safe shutdown loads when power supply
is not available.
Consider a class 10 type of battery where it has a
efficiency of 90%, 300Ah battery.
the effective AH available for the load is 300x0.9=270AH.
For 1 hour duration the discharge current will be 27.0A
which is higher than the required value of 23.5A.
There fore for 2 KVA online UPS having the load of 1600W
with 0.8 pf load, it requires 300AH of 8 nos of battery for
1 hour backup.
| Is This Answer Correct ? | 0 Yes | 2 No |
How do we measure earth fault current in Generator Transformer(20/420kv),Station Transformer(20/11 kv) and Unit Transformers(20/11kv) for our plant system, since these don't have any Neutral earth Fault relay connected to their Neutral Earth? But for Unit Service transformers(11/.433 Kv) we have an Earth Fault Relay connected to its neutral earth.Why is such so?
how the 6.6KV motor can be used with 11KV?
why we use mostly 3-phase but not 4-phase and 5-phase what is the difference between them
What is metering cubical? What is the use?
what is the function of fire alarm system?
What is maximum demand and contract demand?
Impedance relay is directional relay or non directional relay?
How to calculate Maximum Demand from Energy meter Reading.
how can service sitting be setted for MCCB?Example for sittings IR (CURRENT RATING),IS(CURRENT STARTING)IO (current operating)?
Any one Give me formula for to increse the power factor, 0.8 to 0.95, How much the KVAr Required
9 Answers Emerson, Rajshree Sugars, Siemens,
what should be distance between two electrical earthing pit as per i.e.e
what is negative d.c. voltage, why this voltage is used in base transciever station.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)