1) How to calculate battery backup for ups as well as solar
with complete formula elaborately......
Answers were Sorted based on User's Feedback
Answer / kuzhali
ups back up time=(AH rating*volt*power factor)/total load
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / velmurugan, so/d, barcf, kalpa
Consider the 2 KVA online UPS.
specifications are as follows: output voltage: 230V, Pf:
0.8, Load is 1600W. DC bus voltage is 96V.
Now Total output is = 2000 VA
PF of the load is = 0.8
There fore output in watts = 2000x0.8= 1600W.
Efficiency of the inverter is 80% therefore power input to
the inverter will be = 1600/0.8= 2000W
DC current of the inverter section= Watts / Voltage
Consider the fully charged voltage = 13.5X8=108V
The DC bus voltage
up to which the battery can deliver= 10.5x8=84 Volts.
therefore maximum current drawn by the inverter when battery
is in line = 2000/84=23.8A
Now consider the backup required for the load, i.e 1 hour
back up is required to safe shutdown loads when power supply
is not available.
Consider a class 10 type of battery where it has a
efficiency of 90%, 300Ah battery.
the effective AH available for the load is 300x0.9=270AH.
For 1 hour duration the discharge current will be 27.0A
which is higher than the required value of 23.5A.
There fore for 2 KVA online UPS having the load of 1600W
with 0.8 pf load, it requires 300AH of 8 nos of battery for
1 hour backup.
| Is This Answer Correct ? | 0 Yes | 2 No |
what is difference between RCB,RCCB &RCBO?
if two transformers are placed parallel & both have fault impedance of 50KA will it increase or decrease show example?
Is a DC Transformer Possible? if Yes, Then Why, if not Then Why?
what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing
Give accurate definitions for these electric terms: Inductor Inductance Inductive Induction Reactance Reactive Esam Baraka ٢١ ساعة
0.5,1,1.5,2.5,4.0.6.0,10,16 square mm electrical wires how much take maximum current in 50htz
is oil viscosity affect on motor current?
What is the function of neutral CT in transformer? Turn ratio of typical CT for 2MVA transformer ? or relation between full load current of transformer and neutral CT ?
1 Answers Electrical Inspectorate,
what happens when you connect a.c and d.c supplies
We have 2 no. 4MW DG set. and GEB supply. But, we running, only 1 DG set. when we done APFC/Power factor setting : 0.90, then winding temp. Low. but when setting done : 0.83, then Winding temp. increase. WHY Why ? ? ?, plz give me answer.
I want formula to calculate cable size as per load given in kw & amp.I searched many sites but didn't right answer.Plz reply me asap.
41 Answers Armco, BEL, BGS, Biocon, BRB Cable, Crystalline Chemical Industries, DLF, Doshion, Electrical, Gold Roof, L&T, Lanco, MEIL, Oman Cables Industry SAOG, PK Services, Polycab, Sabic, SLV, System Electrical, Tata Motors, UEM, UMIC, Vega, Vertex, Voltas,
How to control motor gearbox speed and friquency? If length of cable and dia given, how to measure the voltage drop?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)