How do we measure earth fault current in Generator
Transformer(20/420kv),Station Transformer(20/11 kv) and Unit
Transformers(20/11kv) for our plant system, since these
don't have any Neutral earth Fault relay connected to their
Neutral Earth?
But for Unit Service transformers(11/.433 Kv) we have an
Earth Fault Relay connected to its neutral earth.Why is such so?
I assume your generator rating is around 250-315MW.
GENERATOR TRANSFORMER IS YN-d1 or d11, 420kv power
transformer is provided with neutral bushing and solidly
grounded to earth system (U,V,W-N). YOU CAN MEASURE THE
EARTH CURRENT WITH CLAMP ON METER.
GENERATOR 20KV OUTPUT IS CONNECTED WITH lv side of
generator transformer by bus duct. there is a voltage
transformer, 2 winding y/y or three winding VT Y/y-
opendelts. This open delts voltage indicate the fault in
20kv system.
Genrator is provided with 90% and 100 % earth fault
ptortection.
Generator neutral is connected with generator neutral
grounding transformer. Generator neutral transformer
primary is connected to genrator neutral point and other N
is connected to earth. at this point ,You can measure earth
current by clamp on meter.
I assume you have a Generator circuit breaker.
Generator bus is 20kv. This sw.gr feed stn tranformer -
20/11kv system.This station 11kv feed the auxilary
transformers. Vector group of this stn transformer is D/d.
Also unit transformer is 20/11kv. this 11kv bus feed motor
and auxiliayr transformers. vector group is also D/d.
your medium voltage operates as isolated ground system
Unit service transformer is 11/.433 , thereforn vector
group is D/yn. your low voltage feeder need a nuetral.
therefore neutral is brought out. three phase 4 wire, and
230v-n .
please send the rating of transformer. we can explain you
more.
| Is This Answer Correct ? | 0 Yes | 1 No |
what is the temperature rise test? explain in brief.with formula.
on which power factor synchronous motor run
How many types oil using in transformer ? How many letars using in transformer..?
what are the functions of current transducer and voltage transducer?
If i connect aload to phase taken from one transformer and neutral from another what will happen.
how calculate busbar size for rated amps, which formula use
Why the transformer rating is denoted in VA rating why not in KW
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
How DC earth leakage currents can be reduced ?
Totally how much power will be consumed in 1 hour cotinuous running of electric train engine?
what is neutral voltage
A 11KV, 1200 A breaker combination fixed in a cubicle for HT motor.Is normally for 11 KV motor fuse is using? if Yes, What range fuse is required?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)