What is maximum demand and contract demand?
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
contract demand is also called billing demand and it is not
likely to be exceeded by the consumer.It is the assured
maximum demand.Max demand is the actually recorded one
during the month and the consumer will be penalized if this
exceeds the CD as per applicable rules formed by the supplier..
| Is This Answer Correct ? | 61 Yes | 9 No |
Contract demand is the demand(load in terms of KVA/MVA)
based on the customer requirement with power supplier as
per the supply agreement. Maximum demand is the maximum
load recorded during the billing cycle (usually a month)as
per the power supplier. Billing demand is the demand
charges billed by the supplier based on maximum demand
recorded and contract demand. It varies depending on the
power supplier. For example in Karnataka state all
Electricity Supply Company under Karnataka Power
Transmission Corporation, bills based on 75% of the
contract demand or maximum demand recorded whichever is
higher in a month.
| Is This Answer Correct ? | 38 Yes | 1 No |
Answer / pepepy
Contract demand is the demand where we are making contract with government that we will not cross the value of contract demand.
Maximum demand is the demand where we are utilizing the electricity maximum on a particular time period.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / harsh patel
Contract demand is the total power (KW or KVA) required by the customers and written agreement done with supplier.while maximum demand is the peak load recorded for intervals of some particular time such as 15 minute or 30 minute.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / s t gokhale
I think ,span of time for which the maximum power is used is also important while defining contract demand. In Maharashtra state, maximum demand for a continuous span span of 30 minutes is recorded in the meters and billed as contract demand.
| Is This Answer Correct ? | 0 Yes | 6 No |
why induction motor always operate at lagging p.f.?
cab we add capacitor bank with generator to improve power factor or not??????
What is the type of electrical earthing recommended in hard rock area
Differentiate between Low and High impedance Protection
Send me Model Question paper for the post Scientific Assistant in NPCIL
why nearly all the voltage levels are in the multiples of 11 like 3.3 ,6.6 ,33 ,11 kv.....
In between UPS out going changer over switch and ups raising main input, both side cable gland producing heat but the cable doesn't get heat,Why?
Arrangement of earthing materials.like what we put first charcol,then salt.then plate. Plz answer me about that.
Which addressing mode contains the address for data as a part of the instruction in 8085.
how to calculate the surge level of surge suppressors related to the SF6 cicuit breakers?
a wire in which bulb is connected there is two terminal when one terminal is connected to phase than why the value of current shock in nutral terminal is max. or large??
What is the Difference Between MCCB & ACB & VCB
58 Answers Absotherm, Delton, Divine, JLL, Jyoti Ltd, Kirloskar, L&T, RPP, Siemens, TCL, TCS, Teekays, YSJ,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)