Any one Give me formula for to increse the power factor,
0.8 to 0.95, How much the KVAr Required
Answers were Sorted based on User's Feedback
Answer / thowsif_emerson_csm team
Calculation of Required Kvar:-
Initial P.f-PFi , Desired P.f-PFd and Real Power of Load in
KW...
KVAR=KW(tanAi-tanAd)
where,
Ai=Cosinverse(PFi) = Initial Power Factor Angle.
Ad=Cosinverse(PFd) = Final Power Factor Angle.
For Example:-
PFi=.85 & PFd=0.9 & Real Load=50 KW
For this required KVAR is 6.7 KVAR....
| Is This Answer Correct ? | 11 Yes | 4 No |
Answer / thowsif_emerson_csm team
Hi Pls Provide me the following Details:-
Input Load in KW....
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / sonam sherpa
P.F = M.D*(Tan(cos-1 x)-Tan(cos-1 y))
M.D - max. demand.
x- Actual power factor
y- Required power factor
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sonam sherpa
in above formual P.F- Capacitor rating in Kvar
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / akhilesh singh
please go through V.K.Mehta's book (power system)
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sk rafiquil islam (kaithi,jamu
p=1.732*v*i*cos phaii so cos phai=p/(1.732*v*i) so,we can decrease of current we can developed pf
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ravi
Hi All,
Can u pls provide me the correct formula to calc.
P.f?????????????????
| Is This Answer Correct ? | 1 Yes | 3 No |
plz tell me in my que,how to connect thw electrical wirening in house?
hi frenz,its aswathy.i hve aplied for the hpcl test on feb,pls send the test patern & the placement papers as soon as possible. mail-id :kjaswathy@gmail.com
what is the uses of C.V.T transformer in switch yard?
is there any pottential in neautral?
How a capacitor discharge weld power supply works? what is the use of a pulse transformer?
How to calculate the Efficiency of Chiller
how to testing the AC 3 phase motor? and what is the test procedure & kits required for testing?
The capacitive reactance of a capacitor of 1/(2(PI)) F at 10^3 H is
Sir,In our company there are 3 caterpillar make(capacity:(1) 3.3KV,2.5MW(2)3.3KV,2.5MW & (3)3.3KV,1.9MW) & 1 deutz make (capacity:11KV,3.8MW)gas engines utilised,all are running in paralell. There are three transformer utilised,(1) 6.25MVA,3.3KV/22KV,Impedence voltage:6.7% used for two generator,both are 2.5MW(2)5.5MVA,3.3KV/22KV,Impedence voltage:7.2% used for one generator of 2.5MW & (3) 5.5MVA,11KV/22KV,Impedence voltage:7.8% used for one generator of 2.5MW.all generator breakers capacity of 1250Amps. Sir,I want the details of fault level calculation of generator,transformer individually & for whole system. If you require any information from me.feel free for contact me sir.pl.send the answer of my question as the earliest as possible.
tell me working of air circuit braker.
What is EMC filter in VVVF Drive ?
Why Utility Distribution System in India is mainly at 11 kV? Why not Utility go for 33 kV?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)