What is the max demand on your transformer and your company?




Answers were Sorted based on User's Feedback



What is the max demand on your transformer and your company?..

Answer / jatinder dhaliwal

max demand of a company and transformer is the maximum
power that his circuit is likely to draw at any time.

Is This Answer Correct ?    38 Yes 2 No

What is the max demand on your transformer and your company?..

Answer / mohd. karim

i want to give answer of this que. by an Example:

**if connected load of our system( factory,
Works,plant ...Etc) is 1250KW(1.25MW)...it means our maxi
demand at PF 0.83 is 1506KVA (1.506MVA)

one transformer used for this load with rating PF 0.8,
11kv/0.415, 1500kva
***it means MD in KW is 1200KW
MD in Kva is 1500KVA (1.5MVA)

it means this x-mer is not suitable for this load because
efficiency of x-mer is maxi. at half load. for above
example, this x-mer is suitable for 600KW-850KW at
PF=0.83)
Here
** is the MD of Company
***is the MD of X-mer

Is This Answer Correct ?    20 Yes 4 No

What is the max demand on your transformer and your company?..

Answer / pablo

The maximum demand of a power transdormer does not exceed
80 percent of its power rating.

Is This Answer Correct ?    14 Yes 5 No




What is the max demand on your transformer and your company?..

Answer / sp singh

Transformer generally selected 25% higher KVA than peak load of the organization.

Is This Answer Correct ?    1 Yes 0 No

What is the max demand on your transformer and your company?..

Answer / gourav00

always 11kv rating power transformer use in my company..n almost 3 phase transformer use

Is This Answer Correct ?    0 Yes 2 No

What is the max demand on your transformer and your company?..

Answer / will

Maximum demand means that it shall not cross the 100%
rating of the transformer, if the transformer has no
colling stages and can take extra demand.
Normally the cooling stages increase the transformer
capacity to take load 33% more at eact cooling stage.
Ist cooling stage FA-1.33%
2nd cooling stage FA-1.66%

That means when the transformer getting loaded more than
100% capacity the ist cooling stage gets automatically on
and when it gets more than 133% loaded the second cooling
stage gets automatically on.

Is This Answer Correct ?    4 Yes 9 No

What is the max demand on your transformer and your company?..

Answer / rajendran.m

750 kva.

Is This Answer Correct ?    5 Yes 12 No

What is the max demand on your transformer and your company?..

Answer / stanley electrician

Consider that 500kva transformer in your company,
and you use only 250 kva load maximum. you must calculate
the increase of your load for the future five years.
That means, expecting 275 kva load in feuture, you will get
upto 300 kvaon maximum demand.

Simply get 25% extra from the maximum load.

Is This Answer Correct ?    5 Yes 13 No

Post New Answer



More Electrical Engineering Interview Questions

Dear Friends, Need your help for connecting APFC panel, Quotation : I have 2 No’s 1000 KVA Transformers, both transformers are having separate APFC panels, ( Tr-1,400KVAR, TR-2,450 KVAR) Now I want to stop One transformer, present load is 650Amps, Max, So One transformer is enough, I have switched OFF TR-1, but PF is not maintaining properly, its 0.5, So now I want to connect TR-2 APFC also in TR-1 Loads, Can any one answer for my Quotation with drawing, how to connect TR-2 APFC panel in TR-1 Loads,

4 Answers   L&T,


which IS or IEC is used for earthing,breakdown voltage of transformer oil, hv/pd testing and all type of electrical testing

0 Answers  


. What should be the minimum and maximum ohmic value for earthing?

1 Answers  


what is 6 pulse and 12 pulse inverter? Explain brifly

2 Answers  


how is the cable tray designed & how its total length is calculated for an Industrial plant Say for Ex. (500KW Motor Load)

0 Answers  






what is voltage gradient?

8 Answers   Bhel,


What is the difference Marshaling box and RTCC (Relay tap changer circuit) Panel of transformer ?

1 Answers  


What are HT & LT Cables? What are their values?

3 Answers   IOCL,


What is class X ct? What rare its uses?

2 Answers  


why need to be maintain power factor for industrial customer?

2 Answers  


what is formula of illumation calculation

0 Answers  


what is the diff.between neutral and earth?

4 Answers  






Categories
  • Civil Engineering Interview Questions Civil Engineering (4646)
  • Mechanical Engineering Interview Questions Mechanical Engineering (3704)
  • Electrical Engineering Interview Questions Electrical Engineering (15794)
  • Electronics Communications Interview Questions Electronics Communications (2638)
  • Chemical Engineering Interview Questions Chemical Engineering (763)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (79)
  • Bio Engineering Interview Questions Bio Engineering (30)
  • Metallurgy Interview Questions Metallurgy (95)
  • Industrial Engineering Interview Questions Industrial Engineering (199)
  • Instrumentation Interview Questions Instrumentation (2884)
  • Automobile Engineering Interview Questions Automobile Engineering (171)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (41)
  • Marine Engineering Interview Questions Marine Engineering (62)
  • Power Plant Engineering Interview Questions Power Plant Engineering (170)
  • Engineering AllOther Interview Questions Engineering AllOther (1336)