What is the max demand on your transformer and your company?

Answers were Sorted based on User's Feedback



What is the max demand on your transformer and your company?..

Answer / jatinder dhaliwal

max demand of a company and transformer is the maximum
power that his circuit is likely to draw at any time.

Is This Answer Correct ?    54 Yes 4 No

What is the max demand on your transformer and your company?..

Answer / mohd. karim

i want to give answer of this que. by an Example:

**if connected load of our system( factory,
Works,plant ...Etc) is 1250KW(1.25MW)...it means our maxi
demand at PF 0.83 is 1506KVA (1.506MVA)

one transformer used for this load with rating PF 0.8,
11kv/0.415, 1500kva
***it means MD in KW is 1200KW
MD in Kva is 1500KVA (1.5MVA)

it means this x-mer is not suitable for this load because
efficiency of x-mer is maxi. at half load. for above
example, this x-mer is suitable for 600KW-850KW at
PF=0.83)
Here
** is the MD of Company
***is the MD of X-mer

Is This Answer Correct ?    25 Yes 5 No

What is the max demand on your transformer and your company?..

Answer / pablo

The maximum demand of a power transdormer does not exceed
80 percent of its power rating.

Is This Answer Correct ?    18 Yes 6 No

What is the max demand on your transformer and your company?..

Answer / sp singh

Transformer generally selected 25% higher KVA than peak load of the organization.

Is This Answer Correct ?    4 Yes 0 No

What is the max demand on your transformer and your company?..

Answer / nagesh.patwari

Maximum Demand (kVA) is your peak demand of electricity from the grid. ... Your energy distribution company charges you for the maximum demand, so it costs you money. Maximum demand (MD) is the peak level of electricity demand recorded by TNB meter during a 30-minute interval in a month. The amount charged to a user is based on the recorded MD in kilowatt (kW) multiplied by the respective MD rate.

Company MD is sanctioned MD which you have to maintain to avoid penalty from Electricity Board

Is This Answer Correct ?    0 Yes 0 No

What is the max demand on your transformer and your company?..

Answer / naveenkumar m

The recorded maxdemand is the maximum demand of transformer

Is This Answer Correct ?    0 Yes 1 No

What is the max demand on your transformer and your company?..

Answer / gourav00

always 11kv rating power transformer use in my company..n almost 3 phase transformer use

Is This Answer Correct ?    0 Yes 5 No

What is the max demand on your transformer and your company?..

Answer / rajendran.m

750 kva.

Is This Answer Correct ?    6 Yes 13 No

What is the max demand on your transformer and your company?..

Answer / will

Maximum demand means that it shall not cross the 100%
rating of the transformer, if the transformer has no
colling stages and can take extra demand.
Normally the cooling stages increase the transformer
capacity to take load 33% more at eact cooling stage.
Ist cooling stage FA-1.33%
2nd cooling stage FA-1.66%

That means when the transformer getting loaded more than
100% capacity the ist cooling stage gets automatically on
and when it gets more than 133% loaded the second cooling
stage gets automatically on.

Is This Answer Correct ?    4 Yes 11 No

What is the max demand on your transformer and your company?..

Answer / stanley electrician

Consider that 500kva transformer in your company,
and you use only 250 kva load maximum. you must calculate
the increase of your load for the future five years.
That means, expecting 275 kva load in feuture, you will get
upto 300 kvaon maximum demand.

Simply get 25% extra from the maximum load.

Is This Answer Correct ?    5 Yes 13 No

Post New Answer

More Electrical Engineering Interview Questions

How good are you in resolving the commercial issues to Employer's advantage?

0 Answers  


there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit

0 Answers  


why ct secondary side shortlink provided? its open what will happen?while running ?

2 Answers   Essar,


why farmers are use earthing instead of neutral for their light conec. at field.is it safe

2 Answers   Honeywell,


What is fault level?How it is calculated and how it is Expressed?

2 Answers  






What is installed in PAC that is control the humidity

0 Answers   Sodexo,


Can motor act as generator (OR) vice versa? explain how does it do please post the answer technically

11 Answers   GM General Motors,


Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.

1 Answers  


how to changeover ups in this power failur time?

0 Answers   Essar,


in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?

1 Answers   DLF,


Why Diffrential and Ref relays are used together although Diffrential relay can protect Pri and Sec of Transformer

1 Answers   Qatar Gas,


Define phase cross over?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)