What is the max demand on your transformer and your company?
Answers were Sorted based on User's Feedback
Answer / jatinder dhaliwal
max demand of a company and transformer is the maximum
power that his circuit is likely to draw at any time.
Is This Answer Correct ? | 54 Yes | 4 No |
Answer / mohd. karim
i want to give answer of this que. by an Example:
**if connected load of our system( factory,
Works,plant ...Etc) is 1250KW(1.25MW)...it means our maxi
demand at PF 0.83 is 1506KVA (1.506MVA)
one transformer used for this load with rating PF 0.8,
11kv/0.415, 1500kva
***it means MD in KW is 1200KW
MD in Kva is 1500KVA (1.5MVA)
it means this x-mer is not suitable for this load because
efficiency of x-mer is maxi. at half load. for above
example, this x-mer is suitable for 600KW-850KW at
PF=0.83)
Here
** is the MD of Company
***is the MD of X-mer
Is This Answer Correct ? | 25 Yes | 5 No |
Answer / pablo
The maximum demand of a power transdormer does not exceed
80 percent of its power rating.
Is This Answer Correct ? | 18 Yes | 6 No |
Answer / sp singh
Transformer generally selected 25% higher KVA than peak load of the organization.
Is This Answer Correct ? | 4 Yes | 0 No |
Maximum Demand (kVA) is your peak demand of electricity from the grid. ... Your energy distribution company charges you for the maximum demand, so it costs you money. Maximum demand (MD) is the peak level of electricity demand recorded by TNB meter during a 30-minute interval in a month. The amount charged to a user is based on the recorded MD in kilowatt (kW) multiplied by the respective MD rate.
Company MD is sanctioned MD which you have to maintain to avoid penalty from Electricity Board
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / naveenkumar m
The recorded maxdemand is the maximum demand of transformer
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / will
Maximum demand means that it shall not cross the 100%
rating of the transformer, if the transformer has no
colling stages and can take extra demand.
Normally the cooling stages increase the transformer
capacity to take load 33% more at eact cooling stage.
Ist cooling stage FA-1.33%
2nd cooling stage FA-1.66%
That means when the transformer getting loaded more than
100% capacity the ist cooling stage gets automatically on
and when it gets more than 133% loaded the second cooling
stage gets automatically on.
Is This Answer Correct ? | 4 Yes | 11 No |
Answer / stanley electrician
Consider that 500kva transformer in your company,
and you use only 250 kva load maximum. you must calculate
the increase of your load for the future five years.
That means, expecting 275 kva load in feuture, you will get
upto 300 kvaon maximum demand.
Simply get 25% extra from the maximum load.
Is This Answer Correct ? | 5 Yes | 13 No |
How good are you in resolving the commercial issues to Employer's advantage?
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
why ct secondary side shortlink provided? its open what will happen?while running ?
why farmers are use earthing instead of neutral for their light conec. at field.is it safe
What is fault level?How it is calculated and how it is Expressed?
What is installed in PAC that is control the humidity
Can motor act as generator (OR) vice versa? explain how does it do please post the answer technically
Why RCD trips on connecting to one Socket but not trips one other circuit on same RCD.
how to changeover ups in this power failur time?
in three 3.5 core aluminium ug cable. one cable is used for one phase by shrting R,Y and B wires and other 2 cables used for Y and b phases. balace 3 neutral wires are made common and connected to load. suddenly neutral current was more than line current what is the reason behind this?
Why Diffrential and Ref relays are used together although Diffrential relay can protect Pri and Sec of Transformer
Define phase cross over?