What is fault level?How it is calculated and how it is
Expressed?
Answers were Sorted based on User's Feedback
Answer / denzel101
Fault level is a value of fault energy realesed under fault
conditions.for example if we have
A 20MVA 66/11KV with a 5% impedance.
Maximum fault MVA will be
20MVA/0.05 = 400MVA
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / sandeep
Generally Fault current is 20 times the actual current
| Is This Answer Correct ? | 2 Yes | 0 No |
can a rotating machine give the DC output without commutator? if yes, how? if no, why?
1.why are not using acb 33kv ht side? is there any problem 2.what is difference between acb,vcb,sf6 breackers? 3.what is the function of invertor and convertor in ups?
how calculated Transformer losses.
why we connect dg neutral with ground?
How to protect sensitive loads such as Dosing pumps inside a factory from voltage surge/voltage fluctuation.
why we are using in reverse power relay in generator singranizing
Why did lightening arrestor solid copper rod head is sharp on mobile tower top?
coil is consist of
In a 11KV 3phase system do you need to earth both sides of the cable?
What is the Impedance, inductive reactance calculations
why rotor current reading is taken & why not stator?
What is mean CT Saturation? How to calculate?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)