why farmers are use earthing instead of neutral for their light conec. at
field.is it safe
Answers were Sorted based on User's Feedback
As there is a vast difference between the Earth & Neutral
The ground or "earth" wire is a circuit's safety protective
wire that normally carries no current.
It is there to force a fuse to blow or a circuit breaker or
GFCI to trip if a fault condition occurs in any appliances,
their flexible cords or plugs that are connected into the
circuit.
By carrying away the excess current in a fault condition -
which should cause the protecting fuse to blow or circuit
breaker to trip - the "ground" or "earth" wire protects the
building and its occupants because the power should be cut
off before anyone gets electrocuted or any overloaded
circuit wiring or appliances catch on fire.
The neutral is the normal "return" wire: in systems where
the load is supplied from only one hot (or "live") wire, the
neutral completes the circuit and carries current back from
the load to the power station.
All the neutral and ground (or "earth") wires in a building
are tied or linked together at the incoming service main
breaker panel. This is the only place they should ever be
tied together because it is "upstream" of all the fuses
and/or circuit breakers protecting the hot (or "live") wires
for the various circuits installed in the building.
Warning: we must never assume that a neutral is safe to
touch: it has to be checked with a voltmeter or a voltage
indicator to be sure it is not "live". This is because a
neutral wire is designed to carry current under normal
circumstances.
So, if a neutral wire going back to the incoming main
breaker panel has not been properly connected - or suffers a
deliberate disconnection or some accidental damage which
causes it to break - then it and any neutral wires connected
to it further downstream will go live up to the break
because of being connected to the downstream loads which
still have hot feeds coming into them!
That is why we should never use a neutral as a substitute
for a proper, separate, ground or "earth" wire.
| Is This Answer Correct ? | 2 Yes | 1 No |
How to find the voltage drop for short,medium,long transmission lines of a 33kv sub-station?
A motor works on 30kw.it is working on 440volts.How much amper will be Required?
Power factor =1.000 at factory in supply. However, PF = 0.8 at motor end. Current = 100 Amp, Voltage = 400 V. What is the power distribution loss? Can I reduce it by adding capacitor at the load feeder?
While elctrical load on DG,capacitor banks kept off why so? If capacitor banks on is their any effect DG?
4 Answers IL&FS Infrastructure Leasing Financial Services,
What are linear elements and non linear elements? and I don't want answers with graph related
How can calculate the rating of a servo stabilizer for given a specific load
Why we are measured insulation resistance applied through DC Voltage?
Why we use a H.T. Fuse from a thick wire, on other side we use high rating of cables? & Why we use less Sq. mm Cable on H.T. side , on other side we use Large Sq. mm cable?
What are the safety measures of Alternator Explain them?
why DC is not generated instead of AC?
Difference between ELCB and RCCB?
in pf lagging means current decrease by increasing voltage is correct or not ? reason ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)