Answer / carl_ellis
Yes, a pneumatic actuator can drive a valve without a
positioner.
In the HVAC world it's done all the time because the service
conditions (temperature/pressure/wear factor) for, say, a
chilled water valve does not necessarily demand the
precision control that a positioner offers.
An I/P (a current to pneumatic transducer) is used to
convert a 4-20mA control signal to a pressure control signal.
The service required in heavy process industries is usually
sever enough that a positioner is used on a control valve.
Company and industry practice will determine the use of a
positioner.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ajaya kumar behera
Yes we can only fully open/close by changing instrument air supply from header valve
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / tickno
yes it can ,but if the bench set of CV is on range 3-15 psi(instrument standadt unit,conversion from 4-20mA to 3-15 psi)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vergel
No, that is why i call a control valve, we need positioner to control the position of the actuator, if its a simple on off valve, no need for positioner...
| Is This Answer Correct ? | 1 Yes | 4 No |
what type of cables are used for f&G systems and detectors, what is the standard colour?
if temperature transmitter is showing wran. sensor 2 fail how can you remove from the transmitter display m/n.3144p rosemount
Calibration of controller (pneumatic)
1.can you use SCADA instead of DCS,DCS instead SCADA 2.Difference between DCS and PLC,can their role be reversed i.e. role interchange 3.Difference between RTU and PLC
0 Answers IOCL, Lakshmi Machine Works,
What is rated capacity in Control valve
-200mmwc to 500mmwc range transmitter have there 4mA is -200 and 20mA is 500.what is the range in 12mA?
diff between neutral ,ground,phase , earthing and shielding?
Difference between ultrasonic flow meter and radar type flow meter
2 Answers Dodsal, Qatar Petroleums,
diff between dead wt calibrator n pressue comparator?
please explain clearly in PID controller if We increase P only what will be action of the contrlere.
why we use 4-20 mA to do calibration of the instruments.why we cant use 0-20 mA?
why we r opening HOT BYPASS valve during startup of a compressor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)