How to calibrate a temperature transmitter & how a Cold junction Compensation will be carried out?
Answers were Sorted based on User's Feedback
Answer / noori
Hi
there are two methodes of temp.tx calibration:
1 - if u have MV sourse u have to get ambiante temp.MV & the
temp. you select and using themocouple vr. MV chart to get
the corresponding MV for these two temps.and for the same
thermocouple type
you have to subtracte the MV for ambiant from the MV for
your temp.
then yiu can inject this new MV to the input of the Tx
you have to get two tempretures for the calibration one for
ZERO &the second for span
you have to do the above prcedure for both points
2 - if you have temperature calibrator the you have to use
the same type of thermocouple immering it directly in the
calibrator and set the first point for Zero & set the second
point for span adjustment
Is This Answer Correct ? | 3 Yes | 1 No |
IF U USE MV INJECTOR FOR THERMOCOUPLE CALIBRATION.........
FIRST U SHOULD MEASURE THE ROOM TEMPERATURE AND TO COMPUTE EQUELENT THERMOCOUPLE VOLTAGE.......V REF....
IF U R INJECTING 100 DEG EQULENT MV U SHOUD DEDECT V REF MV FROM THAT ACTUL MV...AND APPLY ADJUST 100.......
IF U R USING TEMPERATURE CALIBRATOR NO NEED THIS ONE ...U CAN APPLY DIRECT......BECAUSE IT GIVES THE COMBENSATED OUTPUT
Is This Answer Correct ? | 3 Yes | 3 No |
What is stripper & spilitter ? Diffrence in this.?
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
SOME OF YOUR QUESTIONS ARE NOT MAKING ANY SENSE SO TRY AND PUT IN A LITTLE BIT MORE EFFORT BEFORE YOU POST A QUESTION. WE WILL ONLY HELP THOSE WHO WE CAN SEE ARE TRYING TO HELP THEMSELVES.
I want to use 1/2 inch SS316 tube in my high pressure & temperature (64 kg/cm2 & 500 deg C)after condensate pot in pressure tranmistter. 1) Is it possible to use 1/2" ss316 tube in high pressure and temperature line. Tube manufacturer is local vendor. 2)On sarting the plant, We need to do system fluse that time condesate is not in the condesate pot so steam is directly contact with the tube. We have no exact calculation to know our tube is ok or nor at this time. pleae,reply.
dear friends pls tell me how temperature compensations are done in bourdoun tube of pressure guages thankx
what the pid setting in controller
purpose of absolute ppressure transmitter applcation?
hi i'm an Instrumentation student,i have one doubt that we can call- > computer science as CS > Information science as IS > Electronics & communication as E & C In the same way what is short term for Instrumentation....?
On LPG sphere tank we used LIT for level indication.High side port is connected to the bottom of the tank while low side port connected to the top. I would like to know how to fill the glycerin on its low side with two condensing pot installed,one from top and the other one for its drain line.Please I need your expertise...thanks