WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING
INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
Answers were Sorted based on User's Feedback
Answer / kaja farkhan
Calibration is nothing but comparisonof an unknown standard
with an known standard or in other words it is known as
checking the output is proportional to the input or not.
Loop checking is nothing but the instrument installed in
the field must give the signal to the control room without
any break. First in this the continuity of the cable will
be checked from inst to JB in field side and from the JB to
control room.
Is This Answer Correct ? | 15 Yes | 3 No |
Answer / nagabalan
Loop check used to check the Field Instruments activity and
continuity from Field to DCS/PLC.
Field Instruments forced/simulated from filed and value
will be confirmed with DCS/PLC.
For Valves,value simulated from DCS/PLC and position will
be confirmed from the field.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / safeek_psna
I NEED TO SEND THE ANSWAR ABOUT INSTRUMENTAION
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / narenkumar1985
LOOP CHECKING MEANS CHECKING THE CABLE LOOP FROM THE INST TO
MARSHALING PANEL AND TO PLC. WHEN INST GIVING O/P SIGNAL TO
CONTROL ROOM-PLC CHECKING WHETHER THE SIGNAL GOING TO
CORRECT PLC CHANNEL.
Is This Answer Correct ? | 3 Yes | 2 No |
Answer / goldknight3000
Calibration of an instrument is a comparison to a known
standard. Eg. if i need to calibrate a weighing scale, then
we need a known weight for comparison. A known standard
have to be certified by certfying body like NIST.
Loop check is a continuity test coming from/to field to
junction box and junction box to/from Control system.
Is This Answer Correct ? | 0 Yes | 2 No |
how to calibrate differential pressure switch
Control valve Flow characteristic. How the equal percentege curve form?
what is the basic principal of vertax flow meter
3 Answers Balrampur Chini Mill, Saba,
How would you choose differential range?
any body pl suggest me the best type of transmitter for level monitoring of a distillation still which consists of highly corrosive and inflammable liquid.closed vessel height=5000mm especially in petrochemical industries
What is the IEC Standard for PLC I/O Terminal wiring Procedure?
why magnetic flow meter is not used in thermel power plant operation
how to callibrate a new i/p converter
What is SCR?
what is the resource block mode in foundation field but ? what is advantages for this
what is the difference between cold loop and hot loop
what is compensation in engineering and what is temperature compensation?