WHAT IS A CALLIBRATION? WHAT IS MEEAN BY LOOP CHECKING
INCLUDES PRESURE, THERMOCOUPLE,TT,DT?
Answers were Sorted based on User's Feedback
Answer / kaja farkhan
Calibration is nothing but comparisonof an unknown standard
with an known standard or in other words it is known as
checking the output is proportional to the input or not.
Loop checking is nothing but the instrument installed in
the field must give the signal to the control room without
any break. First in this the continuity of the cable will
be checked from inst to JB in field side and from the JB to
control room.
| Is This Answer Correct ? | 15 Yes | 3 No |
Answer / nagabalan
Loop check used to check the Field Instruments activity and
continuity from Field to DCS/PLC.
Field Instruments forced/simulated from filed and value
will be confirmed with DCS/PLC.
For Valves,value simulated from DCS/PLC and position will
be confirmed from the field.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / safeek_psna
I NEED TO SEND THE ANSWAR ABOUT INSTRUMENTAION
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / narenkumar1985
LOOP CHECKING MEANS CHECKING THE CABLE LOOP FROM THE INST TO
MARSHALING PANEL AND TO PLC. WHEN INST GIVING O/P SIGNAL TO
CONTROL ROOM-PLC CHECKING WHETHER THE SIGNAL GOING TO
CORRECT PLC CHANNEL.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / goldknight3000
Calibration of an instrument is a comparison to a known
standard. Eg. if i need to calibrate a weighing scale, then
we need a known weight for comparison. A known standard
have to be certified by certfying body like NIST.
Loop check is a continuity test coming from/to field to
junction box and junction box to/from Control system.
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the solution if rotork motorised control valve showing pink Colour in dcs.
3 Answers Bhushan Power Steel,
how to calculate the total flow in square root
What is the difference between local indicator(flow) and flow indicator?
How to convert Differential pressure to flow in TPH
Is Hart communicator calibration device or communicating device for transmitter?
I need circuit for RTD senser?
How a oxygen sensor & analyzer work at boiler or furnace, what’s the principle & science is beyond this, How O2 sensor scene & convert signal & move toward analyzer & analyzer show reading in percent?
1 Answers GS Engineering Construction, KNIC,
can we change the range of 3151 model level transmitter of rosemount make? present calibration range is 1000mmwc and want to change it to 2000mmwc
how to calibrate differential pressure switch
i/p converter always for supply pessure from 3~15 psi only !! And from where this converter bleed the air.
suppose, after calibrating a transmitter we fixed it in a process line. At live zero condition the Tx shows 4.5 mA. what should we do to make the Tx show 4 mA? If we adjust zero, will it not affect the calibration?
We are used ABB 800xa 5.1.please tell me how to instrall this.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)