flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma
Answers were Sorted based on User's Feedback
Answer / satya
1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / dinesh
the transfer function should have been square root but the transfer function mentioned is linear which is as follows
y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc
so y= (4/375)*x + 12
in order to get correct flow change the transfer function to square root in Tx
| Is This Answer Correct ? | 2 Yes | 0 No |
HOW WE ARE DECIDING WHILE PROGRAMMING IN PID CONTROLLER THAT WE ARE USING HEATING OR COOLING???????
A PLC is programmed to drive three motors A, B and C as follows : After running motor A for an hour, motor B should get ON and motor A should get OFF. And after running motor B for an hour, motor C should get ON and motor B should get OFF. And after running motor C for an hour, motor A should get ON and motor C should get OFF. (That is, a cyclic repetition with time period one hour) Now, the second condition is: If any motor gone faulty and is tripped, the consecutive motor should get ON and the faulty (tripped) motor should be eliminated from cyclic repetition. The remaining two motors should bear the cyclic repetition of one hour each. (For healthy motor take logic as high and for tripped motor take logic as low) Now, the third condition is: When motor A load(Amps) exceeds 60% of its rated load, motor B should get ON in parallel to motor A. And when both motors A & B are running in parallel, and if their load exceeds 60% of their rated load, motor C should also start in parallel to A & B. [Here the cyclic repetition is eliminated, until their loads become normal(40%)] [Take logic high(1) for load at 60% and logic low(0) for load at 40%] Now draw a flow chart or a ladder diagram to fulfill the above condition.
WHAT REASEAN USE TRANSMETER TWO WIRE & FOUR WIRE
please send me some question papers of HPCL aptitude test ?? please send it to bipinb.28@gmail.com ...
how can i calibrate the temperatuture gauge used by temperature bath(dry block) i mean step by step procedure?
what are the different types of Protocols? & their applications.
6 Answers Infosys, Sitara Chemical Industries, Syntel, VSNL,
hello.my friends.i am an electronics & instrumentation engineer.i want to know Q1.why lugs use in instrumentation cable termination? Q2.if limit switch not working what to do?
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
What pressure transmitter.
what is formula mv convert to temperture
What is voltage free(wet) and potential (dry) contact?
why we use negative 24vdc to a proximeter
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)