flow transmitter range is 0 -500 mmwcc but the transmitter
shows 12 ma for o mmwc instead of 4 ma ...how to solve this
problem when we apply 375 mmwc it shows 16 ma
Answers were Sorted based on User's Feedback
Answer / satya
1st ensure the tapping . the root valve. orifice range . tx range . then open the high side , open the low side drain the flow shoude be zero . if not trim the tx. and then. take it online
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / dinesh
the transfer function should have been square root but the transfer function mentioned is linear which is as follows
y=mx+c where m is slope & c is the bias
to calculate slope
m={(y2-y1)/(x2-x1)} where
y2=16ma; y1=12 ma; x2=375 mmwc; x1=0 & C is 12ma at 0 mmwc
so y= (4/375)*x + 12
in order to get correct flow change the transfer function to square root in Tx
Is This Answer Correct ? | 2 Yes | 0 No |
-/5A. What is the meaning and limitations of this in energy meter constant. It is a 3 phase LT Energy Meter. If this Energy Meter is connected through a CT of ratio 200/5 Amps, then what is the multiplying constant and how its will be calculated.
wich is coming the first HAZOP OR SIL
What is an antisurge control system, how it works?
tell me the field & lab calibration procedure step by step with diagram of pressure gauge, pressure switch, pressure transmitter, temperature switch, level switch, flow switch, flow transmitter, temperature transmitter, temperature indicator, flow indicator, level indicator, control valve, thermocouple, pressure indicator (digital & analogue),
I want measure the volumetric flow of gas in waste heat recovery Boiler?Tell me how and which type of instruments required. Plz mail me:naba02222@gmail.com Sam please post the answer .
how to calculate orifice sizing? and tell me if pipe size bet 50mm t0 200mm then we can use pipe flange??? and above 250mm pipe size should i use D & D/2 Flange? is it right or wrong?
HOW TO CONVERT 0-60KG/CM2 PRESSURE TRANSMITTER TO A LEVEL TRANSMITTER? CAN WE ABLE TO DO IT? IF YES HOW TO DO IT BY USING HART?
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
list of flame proof certification ?
pls tell me whethere flame proof HMI's are available or every HMI is manufactured by considering flame proof standard.
What are the Components of Siemens S7 300 Series PLC system ?
What is the absolute temperature