What information needs for Control Valve "sizing"
Answer / laxit - ch2m hill
Line Size, Process parameter ( P1,P2,Flow,Temperature),
Service material properties such as liquid or gas,
MW,SG,Vapor pressure etc. Try to get basic CV value with
equation & then check with the fisher/flowserve/samson etc
vendor sizing software.
| Is This Answer Correct ? | 6 Yes | 1 No |
What is Hysteresis mean in Instrument?
what is the process for double acting cylinder pneumatic for 32' v/v
how to rectify the problem ,if we erected the DPT instrument wrongly of hp on lp side and lp on hp side?
What is output of Thermocouple at 25 deg c
Can SmartPlant Instrumentation be used in a concurrent engineering environment?
What is the formula To convert Degree centigrade to foranhight.
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
what is cold loop? difference between hot and cold loop?
How the flow can be measured by using DP Transmitter?
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
CAN YOU USE MOVING COIL METER FOR MEASURING A.C?
Explain PID controller tuning & any one method used for it.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)