what is the calibration standard for pressure and differential pressure
transmitters?
Answer / jaffer
differential pressure transmitters:
1.both side applied a pneumatic pressure in the h.p&l.p side
check the response on the dp cell.
2.equal pressure on the both side and then transmitters shown
a zero value.
3.upper range value(URL)on the h.p side 10,000mmwc or 1kg/cm2. this value depend on process reqirement.
4.lower range value(LRL)on the l.p side 0 mmwc or 0 kg/cm2.
5.And then change value&change the tag no.
6.check the states of the transmitter. by the help of field calibration devices.
pressure transmitters:
1.the pressure transmitter is only one physical quantity sensing input&applied a input and then same 2,3,4,5,6steps.
| Is This Answer Correct ? | 5 Yes | 0 No |
Can combine control system for Emergency control system (ESD)and Fire & Gas System ( F & G) is possble to built and offer to client? Can such system is as per Norms in India?
The document / drawing that is primarily used in depicting the “Bill of Materials (BOM)” of piping system is the
hi my name is rakesh patel i just complited my be in instrumentation & control now i am going to working as a validation engineer in a poject department so what is a scope in a future as a validation engginer ? what line is good for me can any bady give me complete solution please? your regard rakesh patel
WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider
What is Fieldbus?
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
I have a Control VAlve having size of 2 ".Only the known parameter is Pressure drop . Its 2 Kg. Then How to calculate control valve sizing means Cv.
How to calibrate DP tramitter in flow measurement application? consider my range of flow is 0 to 2000 kg/hr ? please give calculation of , How much pressure applied on low pressure side and high pressure side please give detail of calculation .... It so important for me please reply as soon as possible
what is the formulae to find the thermocouple output to temperature
hello friends, can you please send me the model paper or question paper to be prepared for hpcl examinations????????? You can mail me at rahim_here@yahoo.com waiting for your reply........... help me .. plz.....
An electronic p controller has an input range of 1-5v, and output range of 4-20mA, while testing a step change of 0.4 was applied at the input , the PB setting was 50% ,what should be the change in the output ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)