i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible
Best regards
ikraam haider
Answers were Sorted based on User's Feedback
Answer / s.arunraja
Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels
Regards
S.Arun Raja
| Is This Answer Correct ? | 4 Yes | 0 No |
Answer / sagar khandekar
First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / r.murugan
Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter
boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN
IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ashish mahadik
U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.
| Is This Answer Correct ? | 1 Yes | 2 No |
all types of liquid analyzer principle with drawing?
HOW MANY METHODS OF TEMPERATURE MEASUREMENT ? HOW MANY MEASURING DEVICES / TRANSDUCERS ?
6 Answers Aramco, IOCL, JP Group, NFCL,
how can we measure the level measurement with the help of pressure gauge?
how to connect the HART protocal with control valves
what do you mean by smart instruments?explain with example
what is difference between PLC and DCS?
Is Hart communicator calibration device or communicating device for transmitter?
What is the use instrument barriers? Can you give me review materials about this?
What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?
Hello friends i need check lists of different instruments during the Erection and commissioning in thermal power plant.Please help me.My Mail id is naba02222@gmail.com/naba02222@rediffmail.com Thanks Nabakishore Biswal
in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.
can you give some devices that measure directly the mass flow rate.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)