Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible

Best regards

ikraam haider

Answers were Sorted based on User's Feedback



i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / s.arunraja

Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels

Regards
S.Arun Raja

Is This Answer Correct ?    4 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / sagar khandekar

First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.

Is This Answer Correct ?    2 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / r.murugan

Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter

boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN

IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING

Is This Answer Correct ?    1 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ikraamh5

engineering level

Is This Answer Correct ?    0 Yes 1 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ashish mahadik

U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

all types of liquid analyzer principle with drawing?

0 Answers  


HOW MANY METHODS OF TEMPERATURE MEASUREMENT ? HOW MANY MEASURING DEVICES / TRANSDUCERS ?

6 Answers   Aramco, IOCL, JP Group, NFCL,


how can we measure the level measurement with the help of pressure gauge?

7 Answers   Reliance,


how to connect the HART protocal with control valves

1 Answers  


what do you mean by smart instruments?explain with example

4 Answers  


what is difference between PLC and DCS?

10 Answers  


Is Hart communicator calibration device or communicating device for transmitter?

4 Answers   Yokogawa,


What is the use instrument barriers? Can you give me review materials about this?

1 Answers  


What happen if I install my pressure transmitter below the elevation of pipe in natural gas service?

0 Answers  


Hello friends i need check lists of different instruments during the Erection and commissioning in thermal power plant.Please help me.My Mail id is naba02222@gmail.com/naba02222@rediffmail.com Thanks Nabakishore Biswal

1 Answers  


in my plant 100% feedwater control v/v is air to close but due to instrument air fail,the valve opens but instead of drum level high its get tripped in low low drum level.the urv of level tx is 0 and lrv is -800.pls tell me the reason. for such behaviour.

1 Answers   Sirpur Paper Mill,


can you give some devices that measure directly the mass flow rate.

1 Answers   Takreer,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)