Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible

Best regards

ikraam haider

Answers were Sorted based on User's Feedback



i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / s.arunraja

Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels

Regards
S.Arun Raja

Is This Answer Correct ?    4 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / sagar khandekar

First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.

Is This Answer Correct ?    2 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / r.murugan

Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter

boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN

IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING

Is This Answer Correct ?    1 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ikraamh5

engineering level

Is This Answer Correct ?    0 Yes 1 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ashish mahadik

U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

what is use of communication wire in multipare cable(oil and gas field), why this communication wire not used in single pair cable?

0 Answers  


Why Ma signal is using for control system?

1 Answers   Petrofac,


what is procedure of calibration of remote seal transmiter, botom to top flanch 850mm, fluid liquid density .73, transmiter fixed on a fractionation colum, under vaccume 10mbar

4 Answers  


What is the difference in clamp on type and inline type ultrasonic flow transmitter.

1 Answers  


How does temperature bath work? How does coil gets heated only by applying some current?

0 Answers   Process Control Technologies,


d/p flow transmitter LP side give to pressure.what you geting out put ? how you get(ma)?

6 Answers   ABB,


Q- Which of the following is Close loop system - a-)respiratory System b-)traffic light system c-)washing machine d-)Room heater my option is A, what is our take on option B & C

4 Answers   Sail,


generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?

1 Answers   Indian Steel,


How to Calibrate Transducers? Can you give me a step by ste procedure?

1 Answers  


What are the different types of thermistors used in industries? How to the operation of typical thermistor?

0 Answers  


why is an oxygen sensor used in a boiler stack

2 Answers   HCL,


I am an intru engg frm pune n completing mba marketing in may 2010, what kind of profile would best suit my educational qualifications??? Also, i will move to US in jan 2011, so this job experience should count Over there too 'coz i want to continue workin even there....

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)