i install a DP transmitter of Faugi on drum level of boiler
but i face a problem in it when i engergize the transmitter
the meter shows 0 or 100% no variation in it.the distance
of two points is 19.5 inches, i am in trouble please
suggest me what can i do it's very urgent Please reply me
as soon as possible

Best regards

ikraam haider

Answers were Sorted based on User's Feedback



i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / s.arunraja

Hello Dear first check the Calibration Range of Transmitter,
Range should be -xxx(495) to 0 mmwc. for 0 mmwc 20 mA will
be come.when you fill the water in condensate pot 4mA wii
be come because it's closed vessels

Regards
S.Arun Raja

Is This Answer Correct ?    4 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / sagar khandekar

First check
range of
transmitter if
ok then check
+ve & -ve side
of line if again
ok then check
4-20 mA current
means
calibration if
again ok then
check program
and check scale
range. Follow
these step 100%
confirm solve ur
prblm.

Is This Answer Correct ?    2 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / r.murugan

Dear haider
your transmitter calibration is perfect before charging the tramsmitter you have to fill the water in the condensing pot at low side of the tranmitter

boiler is shutdown condition please confirm DRUM VENT ISOLATION VALVES ARE OPEN

IF DRUM VENT ISOLATION VALVES ARE CLOSE YOU WILL NOT GET CORRECT READING

Is This Answer Correct ?    1 Yes 0 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ikraamh5

engineering level

Is This Answer Correct ?    0 Yes 1 No

i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i enge..

Answer / ashish mahadik

U have to apply WET LEg method for Differental Pressure
type level mesurmetnt.Keep ur wet leg(Lo side of tx always
filled with condensed water.
Put the range in tx.-19.5 inches of WC to 0 inches of WC.
see the result but make sure that ur wet leg should always
filled with water.otherwise ur tx l go to saturation and
give u contunous 20 mamp that is level is full.

Is This Answer Correct ?    1 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

what is plc? breif explain

3 Answers   APL,


WHAT IS THE Differance b/w on/off & pid control valve?

10 Answers  


How 2 calibrate level tank having large height..?

2 Answers  


A DP transmitter is used to measure the level of an open tank. The drain line of the tank is connected to a control valve, and is configured as, if the level of the tank is 90% the valve should get open 10%. And if the tank level is 10%, the valve should get open 90%. Draw wiring diagram and explain how to configure DP transmitter and control valve using HART communicator. If the span error at output is 1%, what will be the %opening of the control valve at 60% level of the tank?

0 Answers  


Which is the best field foundation bus. ( FF ) Yokogawa, Honeywell or others ?

0 Answers   GNFC,






What is possitive and negative feedback?

3 Answers   KNPC,


what is the difference b/w magnetic flow meter&mass flow meter? which one is best?

1 Answers  


what is bevel? why bevel required in orifice plate?

2 Answers  


a laways iface problem with brine level transmitter sealing diaphram a laways giving error and maximum reading i made re range and adjust with side glass but during commission it giving gap reading between it and side glass i need help from expert to explain how to calibrate it. note:dp transmitter yokogawa company

1 Answers  


EXPLAIN PROPOTIONAL INTEGRAL DERIVATIVE CONTROL ACTION?

1 Answers  


How do you measure g's?

5 Answers   Aramco, GNFC, HPCL, Polmon, Thermax,


Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)