what is the formulae to find the thermocouple output to
temperature
Answers were Sorted based on User's Feedback
Answer / ramu
Different Thermocouple will have different mV output for
different temperature.This you have to find out with the
chart supplied.
Is This Answer Correct ? | 9 Yes | 1 No |
Answer / alpesh dalvi
actually in thermocouple relation between temperature & mv
is nonlinear.so there is no specific formula.we are just
take linear range for our use that is thermocouple range.
you can get mv for perticular temperature from the chart.
Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rampal.m.
Output of thermocouple (emf)=a delta T+b delta TSQUARE+------ HERE a=b/10 a&b are constant,where emf is mvolt.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / dilip kumar jha
Temp. = mV * 25.4 ( For K Type thermocouple )
Is This Answer Correct ? | 1 Yes | 0 No |
Explain the burnout feature.
How can we loop powered for a transmitter.How we can do wiring
what is rtd
can you tell me how many stages in steam turbine of 10 MW power plant
How signals can be taken through modbus?
how manys ways dp transmitter can be calibrated having range of -150 to 400mmwc,what side pressure u will apply?
What is the meaning of wet leg
Identification of ss fittings, pilot valves, relief valve.
How to Calibrate Level Troll in field
any body pl suggest me the best type of transmitter for level monitoring of a distillation still which consists of highly corrosive and inflammable liquid.closed vessel height=5000mm especially in petrochemical industries
what does it mean an active front end in vfd plz explain it briefly
modbus and profibus communication difference?