An electronic p controller has an input range of 1-5v, and
output range of 4-20mA, while testing a step change of 0.4
was applied at the input , the PB setting was 50% ,what
should be the change in the output ?
Answer / abhishekk
as PB is given 50%, so Prop gain would be (100/PB)..in this
case it is twice(prop gain)...now as we know for the change
of 1 v in input we get 4ma change in output..so for 0.4 the
change will be 1.6ma WITHOUT using P controller...BUT we
have Prob gain is 2 so change in output will be 1.6*2=3.2ma
hence change in output is 3.2ma
ok..!!!
Is This Answer Correct ? | 18 Yes | 1 No |
i have used level transmitter in starch cooking preparation tank. tank total height 2mtr.sometime LT display shows some error value when tank is fully empty and diaphragm side i already checked okay no problem in diaphragm area. field cable checked 24volt and mA shows correct value while tank empty mA is 4mA. 4mA i needed that 0% but display showing 10% or 15% percentage values are varying continously please give any good solution for me.....
A valve in series with an orifice plate (DP transmitter), is aligned for constant pressure in the pipeline, if there is an error dx, How to align it in process.
plz... clarify my answer, how to calibrate vaccum (DP)leveltransmitter,it is hart. (digital).DETAILS:(coloumn)closedtank height 2650mm,and tx range is 0-1500mmH20.
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
two common seiling liquid used in seal pots are:
Any one can help me to identified, how can we interchange the device in FF
use of split range ? where it is used ? in which control loop it is used ?
I work on a electronic positioner transmitter 4211 at the field.I connect my multimeter in series to get the current output then I calibrate it to 4ma in 0% of position of the valve and 20ma in 100% position of the valve.My problem is in the field I get the correct output current based on my multimeter but in the dcs they only receive 40% in a output 20ma of this positioner.Then I try to simulate in this analog card and they receive the equivalent percent on the value that I simulated.Is ther any possibility to reset the zero and span of this positioner 4211 fisher.And what other possibility I can do to fixed this.This is my email add ( landicho_randy@yahoo.com )
What is the use of double seated valve?
how many type conductivity sensor ?
State 5 different method of level measurements.
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer