WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
Answers were Sorted based on User's Feedback
Answer / lokesh gatty
We cannot control through thermocouple/RTD, they are only
measuring elements,which is connected to temperature
controller which as set value for which point it has to
control temperature (PID/Relay logic control)..Meanwhile
Temperature transemeter is used to convert mv/ohm to anolog
signal(4--20 ma)...we have to refer ohms/mv to degree Celsius
table
| Is This Answer Correct ? | 24 Yes | 1 No |
Answer / aditya kaushik
When we are using the rtd/thermocouple, The output is in mv
or Ohm variation wrt temperature, that will nt be directlyy
processed by our dcs/PLC so we are using transmitters to
convert it to 4-20 ma accordingly, bt now a days rtd cards
are available widely with plc vendors so we can now a days
use directy without transmitters also,\\thnx,
aditya
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / george mathews
Neither temperature transmitter not the thermocouple or Rtd
can control the process. Because as we know Thermocouple and
RTD are nothing but measuring medium , their only work is to
measure the temperature , and for the transmitter it nothing
but a transducer whose only work is to send the measurement
in d form of mA (4 to 20 mA.)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / palanisamy
If you transmit Thermocouple/RTD signal for a longer
distance, it can easily pickup noise & you will not get a
steady reading in the receiving instrument. By providing a
temperature transmitter, we can avoid noise pickup.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / chandrakant kale
WE GENERALLY NEED TO CONTROL THE PROCESS PARAMETER
(TEMPERATURE) SO FOR THAT WE NEED TRANSDUCER.WHICH SEND 4-20
MA TO THE DEVICE WHICH IS TO BE CONTREOLLED. TC IS ONLY FOR
SENSING TEMP.
| Is This Answer Correct ? | 1 Yes | 4 No |
what is RPI and NUT in controlnet networx. what happen if we are increase the NUT of controlnet networx?
hi friends,im an instrumentation and contol engg student,can u hlp me of suggsting barc written question paper,my id is roysuvaranjan@gmail.com, cel no.9563591747
i have calibrate rosemount make level transmitter , wht can i do ? my tank capacity is 30,000 liter
Advantages of servers over normal desktop in PLC SCADA system
what is 24vdc live and dry supply
what is earthing ,grounding in c&i panel?what is the resistance in earthing and grounding of c&i panel?what do u mean by shielding and what is its resistance?
State some of balance principle’ advantages?
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
why we us isolation barrier in hazardous area how it works to protect the area and please clarify its current flow.
Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000
A differential transmitter is calibrated to measure the flow of lquied, explain what wil happen if the fluid is not pure but contains some bubble?
How to measure Flow of air line,what is the procedure of creating DP in line to measure Flow!
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)