WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
Answers were Sorted based on User's Feedback
Answer / lokesh gatty
We cannot control through thermocouple/RTD, they are only
measuring elements,which is connected to temperature
controller which as set value for which point it has to
control temperature (PID/Relay logic control)..Meanwhile
Temperature transemeter is used to convert mv/ohm to anolog
signal(4--20 ma)...we have to refer ohms/mv to degree Celsius
table
Is This Answer Correct ? | 24 Yes | 1 No |
Answer / aditya kaushik
When we are using the rtd/thermocouple, The output is in mv
or Ohm variation wrt temperature, that will nt be directlyy
processed by our dcs/PLC so we are using transmitters to
convert it to 4-20 ma accordingly, bt now a days rtd cards
are available widely with plc vendors so we can now a days
use directy without transmitters also,\\thnx,
aditya
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / george mathews
Neither temperature transmitter not the thermocouple or Rtd
can control the process. Because as we know Thermocouple and
RTD are nothing but measuring medium , their only work is to
measure the temperature , and for the transmitter it nothing
but a transducer whose only work is to send the measurement
in d form of mA (4 to 20 mA.)
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / palanisamy
If you transmit Thermocouple/RTD signal for a longer
distance, it can easily pickup noise & you will not get a
steady reading in the receiving instrument. By providing a
temperature transmitter, we can avoid noise pickup.
Is This Answer Correct ? | 1 Yes | 1 No |
Answer / chandrakant kale
WE GENERALLY NEED TO CONTROL THE PROCESS PARAMETER
(TEMPERATURE) SO FOR THAT WE NEED TRANSDUCER.WHICH SEND 4-20
MA TO THE DEVICE WHICH IS TO BE CONTREOLLED. TC IS ONLY FOR
SENSING TEMP.
Is This Answer Correct ? | 1 Yes | 4 No |
can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)
i have one tank of 500mm height, which is in under vacuum of 735 mmHg, I want measure level of the same using DPT , SO WHAT WILL BE THE URV & LRV, DENSITY OF THE TANK FLUID IS 0.95. is there necessary to fill the LP side with fluid.
why we are using (-24VDC) and where we r using plz tell me
why flow transmitter showing 2.2ma?
Please tell me details about Sox,Nox,SWAS analyser????
Can any body help me,The GE Mark V control system is windows based or Dos based?
Explain PID, ON/OFF, Controls
0 Answers CCIE, Gulf Engineering,
Please anyone answer my question, what is the difference between single acting and double acting control valve, in what condition we better choose single acting rather than double acting
how checking is done in fiber optic cable? explain the working of RTU?
Differentiate between PLC, SCADA and DCS systems
1 Answers Mumias Sugar, SRF, Trimula Industries,
wHAT IS BURST MODE IN TRANSMITTER?
Where we cant instal mass flow meter.