Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD

Answers were Sorted based on User's Feedback



WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD..

Answer / lokesh gatty

We cannot control through thermocouple/RTD, they are only
measuring elements,which is connected to temperature
controller which as set value for which point it has to
control temperature (PID/Relay logic control)..Meanwhile
Temperature transemeter is used to convert mv/ohm to anolog
signal(4--20 ma)...we have to refer ohms/mv to degree Celsius
table

Is This Answer Correct ?    24 Yes 1 No

WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD..

Answer / aditya kaushik

When we are using the rtd/thermocouple, The output is in mv
or Ohm variation wrt temperature, that will nt be directlyy
processed by our dcs/PLC so we are using transmitters to
convert it to 4-20 ma accordingly, bt now a days rtd cards
are available widely with plc vendors so we can now a days
use directy without transmitters also,\\thnx,

aditya

Is This Answer Correct ?    4 Yes 1 No

WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD..

Answer / george mathews

Neither temperature transmitter not the thermocouple or Rtd
can control the process. Because as we know Thermocouple and
RTD are nothing but measuring medium , their only work is to
measure the temperature , and for the transmitter it nothing
but a transducer whose only work is to send the measurement
in d form of mA (4 to 20 mA.)

Is This Answer Correct ?    4 Yes 1 No

WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD..

Answer / palanisamy

If you transmit Thermocouple/RTD signal for a longer
distance, it can easily pickup noise & you will not get a
steady reading in the receiving instrument. By providing a
temperature transmitter, we can avoid noise pickup.

Is This Answer Correct ?    1 Yes 1 No

WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD..

Answer / chandrakant kale

WE GENERALLY NEED TO CONTROL THE PROCESS PARAMETER
(TEMPERATURE) SO FOR THAT WE NEED TRANSDUCER.WHICH SEND 4-20
MA TO THE DEVICE WHICH IS TO BE CONTREOLLED. TC IS ONLY FOR
SENSING TEMP.

Is This Answer Correct ?    1 Yes 4 No

Post New Answer

More Instrumentation Interview Questions

how to calibrate temprature switch and flow switch ?

1 Answers   Adgas,


how can i calibrate a smart temperature transmitter used by druck 720 process calibrator?

0 Answers   Texas,


Which products are available in the Mass Systemswitch and System Manager AC range?

0 Answers  


what is formula mv convert to temperture

4 Answers   Sterlite,


capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?

1 Answers   Gasco,


in the construction field why hook up s.s.tubing for transmitter using upto 6mtrs of closed loop, but y not open loop nomore restriction

5 Answers   Sabic,


Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.

2 Answers  


anybody having Qatar Petroleum questions for instrument Technician offshore ....please send me

0 Answers  


A motor is taking 15 Amps at no load and 60 Amps at full load. and a valve has to open 10% at full load and 80% at no load. How to draw ladder logic.(PLC).

2 Answers  


Dear Sir/Madam, I am attending an interview for ETs in BHEL. I have cleared my written test under Electronics (Instrumentation). This is the first time I am appearing for an interview. Can any one who has attended the interview earlier give me a clue to face the interview. With regards Sindhu

2 Answers   Siemens,


who to convert dc to ac

7 Answers   ONGC,


loop chech tools list

1 Answers   BAP,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)