WHY TEMPERATURE TRANSMITTER USED AS WE CAN CONTROL THROUGH THERMOCOUPLE/RTD
Answers were Sorted based on User's Feedback
Answer / lokesh gatty
We cannot control through thermocouple/RTD, they are only
measuring elements,which is connected to temperature
controller which as set value for which point it has to
control temperature (PID/Relay logic control)..Meanwhile
Temperature transemeter is used to convert mv/ohm to anolog
signal(4--20 ma)...we have to refer ohms/mv to degree Celsius
table
| Is This Answer Correct ? | 24 Yes | 1 No |
Answer / aditya kaushik
When we are using the rtd/thermocouple, The output is in mv
or Ohm variation wrt temperature, that will nt be directlyy
processed by our dcs/PLC so we are using transmitters to
convert it to 4-20 ma accordingly, bt now a days rtd cards
are available widely with plc vendors so we can now a days
use directy without transmitters also,\\thnx,
aditya
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / george mathews
Neither temperature transmitter not the thermocouple or Rtd
can control the process. Because as we know Thermocouple and
RTD are nothing but measuring medium , their only work is to
measure the temperature , and for the transmitter it nothing
but a transducer whose only work is to send the measurement
in d form of mA (4 to 20 mA.)
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / palanisamy
If you transmit Thermocouple/RTD signal for a longer
distance, it can easily pickup noise & you will not get a
steady reading in the receiving instrument. By providing a
temperature transmitter, we can avoid noise pickup.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / chandrakant kale
WE GENERALLY NEED TO CONTROL THE PROCESS PARAMETER
(TEMPERATURE) SO FOR THAT WE NEED TRANSDUCER.WHICH SEND 4-20
MA TO THE DEVICE WHICH IS TO BE CONTREOLLED. TC IS ONLY FOR
SENSING TEMP.
| Is This Answer Correct ? | 1 Yes | 4 No |
Why the industry's standard current standards are from 4mA to 20mA,not from 0mA or any other range?
how to derive kg/cm2 to mmwc? complete derivation.
How is SmartPlant Instrumentation related to INtools?
Can a Differential Pressure Transmitter be used as a normal pressure transmitter??
1)how can calibrate temperature transmitter? 2)how can calibrate flow transmitter? 3)how can calibrate level transmitter?
3 Answers ccic, Emerson, JK Pharma, NIGC, Rockwell, UltraTech,
one rtd sensor which is connected at middle of distillation column where actual temp. is 100deg but when we tight this sensor at thermowell end it goes down to 90 deg & when remove from the thermowell(but sensor end dipped in well) showing actual reading, what is reason?
What is Integral and Derivative control?
please tel me the calibration of pneumatic controler.
What is pipe schedule? What are all effects its having in the valve? how do we take care of pipe sch in case if the customer dint specify in the data sheet. What we need assume and in what basis?
i want use pressure transmitter for flow ,how?
what is the working principle of dis-placer type level transmitter
What is furnace draft control?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)