Answer / carl_ellis
HART communications requires a minimum of 230 ohms to
develop a sufficient voltage drop for the 1200 baud FSK HART
signal to be 'seen' by a HART communicator/modem.
The capacitance in a DC power supply acts as a low pass
filter which filters/strips off the FSK HART data.
Additional loop resistance is needed for HART communications
to take place.
If there is insufficient loop resistance, the HART
communicator/modem will fail to establish HART communications.
In normal field work, it is assumed that the analog input
to which the field instrument is wired will provide the
minimum resistance necessary. Most DCS analog inputs have
an input resistance of 250 ohms. But not all devices do.
And when bench testing/configuring HART instruments it is
not uncommon to connect a DC power supply, but not an analog
input. A HART communicator/modem will not work with just a
power supply powering a HART field instrument. The loop
requires a minimum of 230 ohms.
A 250 ohm resistor is commonly used for a bench
test/configuration because they're commonly available in the
instrument shop.
Carl Ellis
Measure First
| Is This Answer Correct ? | 15 Yes | 1 No |
Answer / carl_ellis
Answer #2 is not correct because the HART communicator is
not an analog input, it does not use a 1-5Vdc signal. A
HART communicator gets and display a transmitter's primary
variable (or other variables) as a digital value; NOT as an
analog value, not as a 1-5Vdc signal developed across an
analog input's resistor. I repeat, HART communications is
NOT analog in nature, it is digital.
The HART Foundation specifies a minimum resistance of 230
ohms, as described in answer #1, in order to develop the
1200 baud HART signal, that rides on top of the DC loop
current signal.
It's easy to prove that 250 ohms (for 1-5Vdc) is not a
requirement for HART communications as a bench test.
Take a 2 wire loop powered HART transmitter, connect a DC
power supply and use a 330 ohm resistor in series in the
loop. The communicator will work and the primary process
variable will be correct. Then try a 470 ohm resistor.
The 470 ohm resistor will work, as well, and the primary
variable will be correct.
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mmuhammad habibullah
hart comunicator read 1 to 5 volt thats why we use 250ohm resistance
in control loop this resistnace already aad in loop
| Is This Answer Correct ? | 4 Yes | 4 No |
what is maximum vaccume?
Can DP transmitter with orifice plate works on Beta ratio 0f 0.3 and differential pressure of 100 MMWC in liquid service application?
what is the input of ph sensor and meter during the calibration time and what is the output?
Why trim span ? How?
What pressure transmitter.
If The RTD(PT100) Show .776 Kohm Resistance the Temperature of process fluid how much?
what is meant by cold junction compensation. where it is used.
if the neutral and ground of ups voltege are connected together in the source itslef then why the voltege b/w neutral and ground comes positive in some other destination inspite of having earth pit. how can we mimmise this?
why is the sleeve of the cable used for?
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
kindly sent some demo question and answer
capillary type tranmitter using remote seals and capillary tubes filled with liquid of known of known density so if you wanna callibrate it just close block valve just before capilary @ high side & connect druck apply it's calibrated range pressure as normal calibration ensure low side block valve must be closed & if you asking commissioning so this is not a DP type pressure tx so simple if you wanna put in servie this tx just open high side block valve & than low side block same way i do it but still transmitter showing -13 ma.just tell me what i want to do ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)