Why we use 250 ohm resister in series
hart communicator?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
HART communications requires a minimum of 230 ohms to
develop a sufficient voltage drop for the 1200 baud FSK HART
signal to be 'seen' by a HART communicator/modem.
The capacitance in a DC power supply acts as a low pass
filter which filters/strips off the FSK HART data.
Additional loop resistance is needed for HART communications
to take place.
If there is insufficient loop resistance, the HART
communicator/modem will fail to establish HART communications.
In normal field work, it is assumed that the analog input
to which the field instrument is wired will provide the
minimum resistance necessary. Most DCS analog inputs have
an input resistance of 250 ohms. But not all devices do.
And when bench testing/configuring HART instruments it is
not uncommon to connect a DC power supply, but not an analog
input. A HART communicator/modem will not work with just a
power supply powering a HART field instrument. The loop
requires a minimum of 230 ohms.
A 250 ohm resistor is commonly used for a bench
test/configuration because they're commonly available in the
instrument shop.
Carl Ellis
Measure First
Is This Answer Correct ? | 15 Yes | 1 No |
Answer / carl_ellis
Answer #2 is not correct because the HART communicator is
not an analog input, it does not use a 1-5Vdc signal. A
HART communicator gets and display a transmitter's primary
variable (or other variables) as a digital value; NOT as an
analog value, not as a 1-5Vdc signal developed across an
analog input's resistor. I repeat, HART communications is
NOT analog in nature, it is digital.
The HART Foundation specifies a minimum resistance of 230
ohms, as described in answer #1, in order to develop the
1200 baud HART signal, that rides on top of the DC loop
current signal.
It's easy to prove that 250 ohms (for 1-5Vdc) is not a
requirement for HART communications as a bench test.
Take a 2 wire loop powered HART transmitter, connect a DC
power supply and use a 330 ohm resistor in series in the
loop. The communicator will work and the primary process
variable will be correct. Then try a 470 ohm resistor.
The 470 ohm resistor will work, as well, and the primary
variable will be correct.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / mmuhammad habibullah
hart comunicator read 1 to 5 volt thats why we use 250ohm resistance
in control loop this resistnace already aad in loop
Is This Answer Correct ? | 4 Yes | 4 No |
what is maximum vaccume?
How to zero trim the level transmitter by using foundation fieldbus communicator.
how to solve temperature error in compressor?
Difference between ultra sonic flow meter
flow transmitter range is 0 -500 mmwcc but the transmitter shows 12 ma for o mmwc instead of 4 ma ...how to solve this problem when we apply 375 mmwc it shows 16 ma
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
How servomotor controls throttle valve of TURBINE?
if we have 380 KVA DG. how to calculate Power Factor. With detailed formula
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?
How to calibration a control valve?
how can calibrate pressure transmeeter in the feild ?
What is negative range in transmeter?